    Furnace runs 24/7

    I have a goodmas gas furnace and is constantly running day and night it is set 70 all the time it is producing warm air so the house is warm all the time... is it normal for it to be running all the time... and if not what ismy problem..
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jan 26, 2009, 07:29 AM
    It all depends upon how cold it is outside and the square footage of the home and the size of the furnace. It seems this winter with the very cold weather many furnaces are running all the time to keep up.
    cornerstonehvac's Avatar
    cornerstonehvac Posts: 26, Reputation: 2
    New Member
     
    #3

    Jan 26, 2009, 07:47 AM

    If it is not over heating your house , the fan relay may be bad causing the fan to run all of the time.On your thermostat is the fan switch set to auto or on? If it is set to on then turn it to auto so that the fan only runs when it needs to heat or cool.
    kinky's Avatar
    kinky Posts: 6, Reputation: 1
    New Member
     
    #4

    Jan 26, 2009, 03:52 PM

    Yes it is on auto.. but I looked at thermastat and it has bateries inside 3 double a is it possible that may be getting week... or is it possible that the furnace may need cleaning..
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Jan 26, 2009, 04:51 PM
    If the furnace is running all the time but the temperature never goes up past the thermostat setting then it is just the blower running all the time. Low batterys will not cause the blower to run all the time but a defective fan control or relay in the furnace will.
    cornerstonehvac's Avatar
    cornerstonehvac Posts: 26, Reputation: 2
    New Member
     
    #6

    Jan 27, 2009, 06:01 AM
    Yes, it sounds like your fan relay is defective. I would have someone come out and rerplace it.
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #7

    Jan 27, 2009, 12:11 PM
    Either the furnace is to small,, or you are in need of doing some insulating
    cornerstonehvac's Avatar
    cornerstonehvac Posts: 26, Reputation: 2
    New Member
     
    #8

    Jan 27, 2009, 04:14 PM

    $5.00 Says the fan relay is bad, been there fixed it a million times. Never will I claim to be perfect cause I've been wrong before. But I'd rather spend a little for a fan relay first than spend a bunch of money on Insulating to find out that it was the relay. But that's just me!
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #9

    Jan 27, 2009, 04:23 PM
    Quote Originally Posted by cornerstonehvac View Post
    $5.00 Says the fan relay is bad, been there fixed it a million times. Never will I claim to be perfect cause I've been wrong before. But I'd rather spend a little for a fan relay first than spend a bunch of money on Insulating to find out that it was the relay. But thats just me!
    If you're wrong, you're going to need someone to give that $5 to. I volunteer my services.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #10

    Jan 27, 2009, 04:36 PM
    Quote Originally Posted by kinky View Post
    i have a goodmas gas furnace and is constantly running day and night it is set 70 all the time it is producing warm air so the house is warm all the time....is it normal for it to be running all the time.....and if not what ismy problem..
    Are you sure its running 24/7. or is it kicking on and off, just on more than off? Need to know if just blower is running, or if gas is firing also. How old is your furnace. How cold is it outside, how many chucks would a wood chuck chuck if a wood chuck could chuck wood(sorry about that, just felt like my questions were getting boring).. Any way, please give us some more info, and we will do our best to help. Model and serial of furnace would help also.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Goodman furnace GMNT080-4 furnace runs good for a while then has to be manually reset [ 5 Answers ]

I have a Goodman GMNT080-4 (90%). I'm having the same problem As Streatherg did back in the Nov 2006 question. I reviewed his article and tried Every thing on there but seems to be doing the same thing. The furnace kicks on for about an hour then locks out and has to be manually reset threw...

Gas furnace runs constantly [ 3 Answers ]

This relates to a problem I'm having with my gas furnace. I took a power hit and ever since then the blower on my furnace continually runs when I have the thermostate set at off and fan on auto. I repalced the thermostate no help. I did notice the fan runs slightly faster when I switch it from auto...

Furnace fan only runs for 30 seconds [ 5 Answers ]

I have a gas furnace in our home. Recently the furnace gas preheats and the fan comes on but only will run for 30 seconds, when the gas reignites the fan turns off. I changed the filter but that made no difference. I looked at the fuses and while looking discovered the that the hot and common wire...

Furnace runs sporadic - on and off all night [ 10 Answers ]

I have an older furnace (20+ years) and it is keeping us up at night. We had some extra ducts put in when we finished the basement and at the time we were right at the edge of what the furnace could run (it is approx 55% effecient). The house is always cool and not a lot of heat reaches the...

My furnace runs all day [ 3 Answers ]

The burners fire for a minute or two at most then turn off for a minute or two. This repeats all day and it won't get above 64f in the house.


View more questions Search