    Can plumbing be vented through the side of house rather than the roof?
    We are rebuilding an old farm house and have a new steel roof. We hate the idea of putting holes in a roof that doesn't leak! Trailer vents are installed inside walls can the vents be put through the wall of the bath rooms rather than through the ceiling and roof?
    Milo Dolezal's Avatar
    Milo Dolezal Posts: 7,192, Reputation: 523
    Plumbing Expert
     
    #2

    Jan 24, 2009, 12:48 PM

    No, vent has to terminate at least 6" above the roof line. You can run your vent surface mounted, on the outside wall and terminate it above the eve.
    paintrocker's Avatar
    paintrocker Posts: 2, Reputation: 1
    New Member
     
    #3

    Jan 24, 2009, 01:44 PM
    Quote Originally Posted by Milo Dolezal View Post
    No, vent has to terminate at least 6" above the roof line. You can run your vent surface mounted, on the outside wall and terminate it above the eve.
    Thanks Milo for your quick response. Reading your other replies is the reason I signed up!
    What if we terminate the pipe through the wall to the out side with a check vent, but under the eve? We have large eves on the east side (one of the vent locations) and putting a pipe up the wall the over the eve would look pretty strange.
    Thanks again for your help..
    Milo Dolezal's Avatar
    Milo Dolezal Posts: 7,192, Reputation: 523
    Plumbing Expert
     
    #4

    Jan 24, 2009, 02:57 PM

    I agree, surface-mounted plumbing is an eye-sore, but can be utilized in certain situations. That's why I thought I should mention this option as well...

    There is a problem with check valve on vent:
    1. Vent not only allows air inward during flush but also is a gravity vent for sewer gases which slowly raise through the venting system to the outside. If you have more vents around your house, especially those venting major plumbing fixtures, than you could, perhaps, get away with installing AAV vent on small fixture, like sink. Check with your Plumbing Inspector if this type of vents are allowed.

    2. Sewer gases will accumulate bellow the eves. Sewer gas will hang there until it is blown around the house by winds. It will smell around your house like sewer. Also, sewer gas will enter your house via open doors and windows. Wider eve, bigger problem.

    It is not such a big deal to properly install vent through metal roof. I am sure sheet-metal guys that installed your roof do it all the time.
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #5

    Jan 24, 2009, 03:22 PM
    Milo gave you UPC. Where do you live?:
    What if we terminate the pipe through the wall to the out side with a check vent, but under the eve?
    My code sez that you may terminate out the wall but not under the eves and with a screen instead of a AAV,(check valve)

    Sections 1404.4 and .5 Of the Standard Plumbing Code, (Extensions Through Wall) allows you to extend vent terminals through a wall providing that,
    1- No vent terminal shall be located directly beneath any door, window or other ventilating opening of the building
    2- No vent shall be located within 10 feet horizontally of such a opening unless it's at least 2 feet above the top of such opening.It goes on to say, they shall be screened and shall not terminate under the overhang of the building.
    In short, you may connect to a existing roof vent that goes through the roof but you must stay away from all openings. Good luck and thank you for rating my answer. Tom

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Clean out of the roof plumbing vent, how to? [ 7 Answers ]

What is the best way to clean out the plumbing roof vent? My toilet flushes too slowly and there is no obstuction in the toited itself causing it. I think it is the roof vent that may be clogged. What is the most advisable and effective method to clean it out? Is putting water from a garden...

Plumbing vent height above sloped roof [ 6 Answers ]

How high should the plumbing vents be above there roof? I have a main vent and a sink vent and both are only 6" high above the roof. The slope is about 4" high for every 12" horizontal. Thanks John G.

How do I locate the main drain pipe for plumbing on the roof of my house [ 1 Answers ]

I need to find the pipe on my roof that I can run water through with a garden hose to try and clear a clog in my pipes to the kitchen. There are two sets of pipes on the roof and each set has two pipes sticking up, one being shortter than the other.

Can the venting pipe for house plumbing be put through a soffit instead of the roof? [ 8 Answers ]

Can I vent my house plumbing through the soffit instead of through the roof?:confused: Hear is why... I have a standing seam roof on my house and my vent pipes have been taken out about 8 times due to snow & ice build up. We thought we finally had it resolved, we had put up braces we had made &...

Plumbing vent to roof [ 1 Answers ]

While trying to run a snake down the roof vent, the darn thing came completely out of the spindle and the snake fell down the vent. Now I have 14' of snake down the darn vent and can't see the free end. Is there some obvious tool I can find or rent that will allow me to fish the thing out? ...


View more questions Search