    350mav optimal blower off delay
    Does anyone have the REAL theory on the blower off delay? What is the most efficient gas, $$ and equipment saving methodology to set the blower off delay?

    Old 2000 sqft house, 2 story, 4" walls, half assed insulated, 90% bryant 350mav propane furnace cycles every 15- 20 minutes. Outside temp 30 deg. Furnace mounted inside house, pulls air in withing 3' of blower. Flexible slinky 8" insulated ducts in crawlspace with footing vents blocked with styrofoam.
    Furnace has selectable blower off delay of 90, 135, 180 and 225 seconds, comes from factory with 135 default.

    Thermostat set at 70 deg.
    Heat rise is 108 deg. At vents.

    When tstat signals off, heat drops
    At 60 sec. 90 deg. At vent, feels luke warm
    At 90 sec. 83 deg. At vent, feels cool
    At 135 sec. 78 deg. At vent, feels cold
    At 180 sec. 75 deg. At vent, feels cold
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #2

    Jan 22, 2009, 04:30 PM

    The blower off-delay is adjustable and applies to heating AND cooling. Typically, the bigger the unit/system, the longer the off-delay. This is to take advantage of the "residual" heating and/or cooling effect. In most applications, the factory default of 90 seconds is optimal. Very "pursuant" on your part to actually measure/time the heat output during the off-delay period. You no longer qualify as a "typical" homeowner. ;)

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Delay-off for furnace main blower when using A/C [ 12 Answers ]

Re Lennox G23Q2/3-75-2 with HS25-311-1P A/C: The built-in delay-off for the blower works well with the furnace, but there seems no easy way to set up a delay-off for the blower when using the A/C. Right now I've connected the low blower wire to the CF terminal on the BCC2 blower control. This...

Bryant 350MAV inducer housing leaking [ 6 Answers ]

I have a 13 year old Bryant 350MAV gas furnace. The 2 halfs of the inducer housing are leaking water. Can these 2 half be pulled apart and resealed? If so what special type of silicone needs to be used if any?

Bryant 350MAV only runs in the mornings [ 6 Answers ]

Hi Everyone, I have a strange intermittent problem with my Bryant 350MAV furnace that has arisen in the last couple of months, since the weather started to cool here in Los Angeles. I usually turn off the thermostat at night when I go to bed, then manually turn on the heat in the morning when...

Bryant Model 350MAV Furnace [ 3 Answers ]

Hi, I recently had a furnace repairman in who told me our inducer on our Bryant Model 350MAV furnace needed to be replaced. He said the total cost would be $1075.00, including $890.00 for the inducer. This seemed high to me. Can anyone give me an idea of what this repair should have cost,...


View more questions Search