    Watt
    I am trying to figure out how many watts per square foot I have in some of my offices using the amps and volts to the breaker box. This is commercial space so the voltages and amps are higher than resindental.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Jan 20, 2009, 03:21 PM

    Your boxes might be 208/120 and a 3 phase 208 box. Some voltages may even be higher such as 277 for lighting and 480V 3 phase.

    The problem with your calcs. Is breakers don't add up to what the main is.

    You could take your main such 200 A single phase 120/208 and compute the power.

    120 V * 200A * 2 or and
    208 * 200; this would be lower

    Outlets which would be the same as residential typically 120V and span multiple sub-spaces.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Watt Capacity of a 15 amp circuit [ 3 Answers ]

How many watts can be in use on a 15 amp circuit?

How many 20 watt lights on a 20 amp circuit? [ 21 Answers ]

I have a 20 amp 120 volt circuit. I have been told that load for a breaker should be 85% of rated capacity and that the formula for determination of required amperage is A=W/V. If this is correct it appears the 14 20 watt undercabinet lights I need would total 2.33 amps. Is this correct? If...

How many amps can I run on an 800 watt inverter? [ 1 Answers ]

Hello, I would like to know how many amps I can run on an 800 watt inverter. I am using mini Christmas lights, Coleman 800 watt inverter and a deep cycle 12 volt battery. Thanks, Steve

Watt capacity on a 20 Amp line [ 1 Answers ]

Anyone know how many watts a 20 Amp line is rated for? I have two 1500 watt commercial grade hot plates (total 3000 watts) that I want to run on a dedicated 20 Amp receptacle (and yes it is a true heavy duty 20 amp recepticle). Thanks JPM71299

Wiring 3 150 watt bulb in parallel [ 1 Answers ]

Hi Will twin 0.75mm flex be OK. There will be less than 3 feet of flex in total. The fittings are porcelain so no earth. Supply is uk, 240v. Thanks