Ask Experts Questions for FREE Help !
Ask
    jrock7897's Avatar
    jrock7897 Posts: 8, Reputation: 1
    New Member
     
    #1

    Jan 20, 2009, 09:57 AM
    New heat pump old t-stat wiring
    Moved in to a home that used to have a package heat pump unit that the owner sold, got a tempstar 3.5 ton with heat pump (ph5542akaz) hooked up all electric, but ran into trouble with old thermostat already installed (white rodgers-1f56n-444) have 6 wire in wall only 4 were hooked up. Can some one give me a start from scratch diagram the wire colors I have to work with are red, yellow, green, white, brown, and blue. The unit calls for orange, I used the blue in the wall hooked up to the "0" terminal (now 5 wires hooked up) and everything seems to work but the air from the vent is warm at best.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jan 20, 2009, 11:30 AM
    Ph5542akaz This is not a model number
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #3

    Jan 20, 2009, 11:32 AM
    The thermostat you picked will not work for a heat pump with electric or gas heat as the second stage. I am sure you should have electric or gas back up since it is very rare to install a heat pump without it. BTW the wiring specifications are also on the link.

    http://www.white-rodgers.com/wrdhom/.../0037-6881.pdf
    jrock7897's Avatar
    jrock7897 Posts: 8, Reputation: 1
    New Member
     
    #4

    Jan 20, 2009, 11:48 AM
    It is a tempstar PH55 series 10 seer package unit with heat strips 3.5 ton this is there model number PH5542aka. How did the previous owner have a heat pump (almost identical unit installed by ac tech) hooked up on this t-stat. went over to his house many times and was working with no problems
    Attached Images
  1. File Type: pdf ph55.pdf (237.2 KB, 617 views)
  2. hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Jan 20, 2009, 01:38 PM
    how did the previous owner have a heat pump (almost identical unit installed by ac tech) hooked up on this t-stat.

    I have no idea unless the heat pump does not have any electric heat in it. If it does not have any electric heat then just follow the diagram for the thermostat and the units terminal letters for the thermostat wiring.. It is very simple if it does not have any additional electric heaters installed in the outside unit.

    NOTE you are not going to have real hot style heat from a heat pump UNLESS it has additional electric heaters installed in it.
    jrock7897's Avatar
    jrock7897 Posts: 8, Reputation: 1
    New Member
     
    #6

    Jan 20, 2009, 01:46 PM
    It does have 9600 watt heat strips but the old one did also he paid around $400 to have them installed. This would be the electric heat right?? Can you tell me which t-stat to buy and how I should wire it the unit I got was used and the low volt wires were just a tangled mess but I used the wire diagrams to sort it out... I think... I'm still confused to where the orange hooks up is it be terminal or o terminal?
    jrock7897's Avatar
    jrock7897 Posts: 8, Reputation: 1
    New Member
     
    #7

    Jan 20, 2009, 01:50 PM

    Is there a way to wire it to bypass the heat strips till I get the new t-stat, I don't need a lot of heat, I'm in Florida but it has gotten to around 30 degrees lately and if this could get a little heat for now it would be nice
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #8

    Jan 20, 2009, 01:57 PM
    First off the unit will need a 50 amp minimum ampacity circuit and a 60 amp breaker for the electric heat. It will also need a circuit for the heat pump section. You better check your 240 volt wiring before you hook up any thermostat. The wiring is listed in the spec cut sheet you provided in your link.

    What the link did not contain was the low voltage wiring hookup. I have no idea what you have there now in the tangeled mess but you said you used the wiring diagram somewhat so you have the diagram and I do not so my suggestion is to follow the diagram. The orange hook up depends upon weather the heat pump reversing valve coil is activated in the A/C mode or heat pump mode. That is a guess if it is not on the wiring diagram. If you try it one way and it does not work then it will stay in the A/C mode so just change it.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #9

    Jan 20, 2009, 02:12 PM
    is there a way to wire it to bypass the heat strips till i get the new t-stat,

    Yes just unhook them from the power source.
    jrock7897's Avatar
    jrock7897 Posts: 8, Reputation: 1
    New Member
     
    #10

    Jan 20, 2009, 02:15 PM

    Have a 50 amp breaker #6 thhn copper feed to ac unit, and separate 60amp breaker #6 thhn copper feed to 60 amp internal breaker inside unit for heat, I have the manual for the installation but it is to big to upload I'll see if I can find the link. The t-stat wires in the unit are hooked up as green to green (fan?) red to red (24v transformer?) yellow to the two yellows in unit (compressor?) white to the two whites in unit (heat?) and grey, brown, blue wired togeather in unit not to t-stat wire. that is what I got from the wiring digram let me know if it is wrong. I had the orange left over (reversing valve ?)
    In the t-stat I wired like this green to g, yellow to y, white to w, red to rc has jumper to rh, previous installer moved factory yellow jumper from why to a (?) and I tried hooking orange from unit to o on t-stat but had no change
    jrock7897's Avatar
    jrock7897 Posts: 8, Reputation: 1
    New Member
     
    #11

    Jan 20, 2009, 02:27 PM
    http://icpindexing.mqgroup.com/docum...2701100401.pdf
    jrock7897's Avatar
    jrock7897 Posts: 8, Reputation: 1
    New Member
     
    #12

    Jan 21, 2009, 06:28 PM

    Can anyone suggest a decent priced digital t-stat that will work with my package ac/heat pump/heat strip unit.
    jrock7897's Avatar
    jrock7897 Posts: 8, Reputation: 1
    New Member
     
    #13

    Jan 29, 2009, 09:08 PM

    Got the ac/heat pump working fine for now without the aux. heat strips but don't know what to set the anticipator at, the instructions for the unit say to set it at what the t-stat instructions call for, and the t-stat instructions say to set it at whatever the unit calls for?? It is set at .4 and is adjustable from .15 to 1.2

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Heat pump programmable stat [ 5 Answers ]

I have a Lennox Heat Pump and want to install a programmable thermmostat for a 2 stage heat pump. I have a 8 wire hook up. O-G-Y-R-B-Br-Bl-W. Which kind of stat should I get.

NO HEAT! Janitrol heat pump and AC system. Changing to Lux Thermostat. Wiring issue. [ 11 Answers ]

I have a Janitrol A/C and heat pump system. I replaced the thermostat with a Lux T9000LC The A/C works fine, but the heater does not. I have it wired as follows: G - Green Y - Yellow W - White RH - Pink B -

Trying to hook up T-stat to a whalen heat pump (model W602E) [ 1 Answers ]

I am trying to hook up a Honeywell RTH7000 to a whalen unit Model # W602E. The wiring diagram has faded to the degree of partial readability. The unit has 6 wires red, blk, brn, yellow, blue, orange I have: red to R Blk to C Brn to G (fan) Yell to Y1 ...

Goodman unit heat pump connecting toRTH7400 stat [ 1 Answers ]

Installed new units 2 1/2 ton goodman units, installed factory 14.25 kw heating element. My biggest problem is the low voltage wiring. The indoor unit has 5 wires coming out they are red,green, white, brown, blue. The outside unit has 5 wires also, blue, white, orange, yellow, red. The cond....

Wiring T-stat to control heat lamp [ 14 Answers ]

I would like to heat an area (128cf with no moving air) using a 1500W heat lamp(s). I would also like to control the temp. inside this space with a standard home T-stat. mounted inside the area being heated. I understand the T-stat uses 24v while the heat source is 120v. I would also like to add a...


View more questions Search