    truckermenchen's Avatar
    truckermenchen Posts: 1, Reputation: 1
    New Member
     
    #1

    Jan 18, 2009, 05:36 AM
    My new heating zone is not working
    I just plummed a new heating zone to my boiler to heat my basement. I am using hot water baseboard. I have power going to my circulator pump, and it is running, but my baseboards are not getting hot. The pipes feel hot a few feet above the circulator, but cold any further away. Is it possible that I am missing a step? Thanks.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jan 18, 2009, 06:31 AM
    I hope you installed bleeders on the baseboard heat you have to have a way to get the air out. Also check the boiler water level/altitude. Make sure the new zone valve is opening if so equipped.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Dual Zone heating [ 4 Answers ]

We have been having problems with our dual zone system, operated by two Simple Comfort 3001 thermostats. When both systems are on, the temperature in one of the zones (typically upstairs when heat is running, downstairs when airconditioning is running) will exceed the limit for that zone, but the...

Zone heating. One zone won't turn furnace on. [ 3 Answers ]

Hi All, I am using two Honeywell V8043E1012 motorized valves. One zone works but the other one you hear the thermostat click on when you raise the temp but the furnace does not come on. When I use the lower floor thermostat the furnace turns and I get heat upstairs. Is this the problem of the...

Heating Zone not working [ 4 Answers ]

It's heating season again and I have a 6 zone hot water heating system and one zone is not working suddenly. It was working fine the other day and today the zone pump will not go on. The thermostat appears to be working fine as it is calling for heat. Is there a procedure that I can follow to...

New two zone heating system not working. [ 1 Answers ]

We are about to close on a new condo and we had a two zone system put in. The problem is when the heat is off upstairs and the temp is set around 70 in the lower level the temp in the upper level reaches 74 or higher and you can feel the heat coming out the vents. The contractor says this is...


View more questions Search