 |
|
|
 |
New Member
|
|
Jul 26, 2006, 03:09 PM
|
|
Entrance cable
How do I cover the electrical service entrance cable attached to the side of my house? What do I use? The original covering has worn out in spots, exposing wires beneath. Also is this something a dummy can do?
|
|
 |
Uber Member
|
|
Jul 26, 2006, 03:47 PM
|
|
Covering the cable will only cover a potential serious problem.
If the sheathing of service entrance cable is damaged, replacement of the entire cable is the only proper action allowed. Replacing the cable will involve contacting the utility company to cut the service to the building to de-energize the cable for removal.
They will return to reconnect service once the new cable is installed and inspected by the local electrical inspector. Some utilities actually do the inspection for the local official.
|
|
 |
New Member
|
|
Jul 27, 2006, 05:35 AM
|
|
This answer is far more complicated, expensive, and inconvenient than I imagined. However, I greatly appreciate your expert free consultation. The thing is, I know I wouldn't go through this involvement with the power company during the summer, when there are frequent power outages. I'd have to wait my turn to have my power resume, resulting in spoiled food, and other losses. So, is there something I can cover the cable with until cooler weather in the Fall, when I'd follow your advice? Maybe electrical tape will do the trick?
|
|
 |
Uber Member
|
|
Jul 27, 2006, 06:12 AM
|
|
A good wrapping with a good quality electrical tape will certainly be better than exposed wires... but note:
If just the outside cover is worn through, and the individual wires still have covering on them, then the electrical tape will certainly be a good "band aid" for now.
But if your individual wires are exposed, you are flirting with disaster to just cover them with electrical tape.
|
|
 |
Uber Member
|
|
Jul 27, 2006, 05:15 PM
|
|
I think it is certainly worth calling the utility to find out how and when this can be done may help you decide if waiting is necessary, or you may discover that they will schedule the disconnect and reconnect the same day. Replacing the cable will only take an hour or so.
The longer you wait, the more damage is being done, rain water is being allowed to migrate into the meter socket and possibly down into the panel. Once this happens, both will need to be replaced.
Thou I do not recommend any temporary repair, should you decide to attempt to apply tape onto the cable, I suggest that you wear insulated gloves rated for at least 250 volts. Coming in contact with the wires can potentially cause you injury or death. Be sure to have someone nearby in the event there is an accident.
If the damage noticed by a utility company meter reader, he has the authority to call out the line truck immediately and have your service cut from the grid as a safety measure, and then call the local inspector to issue a summons to repair before power is restored.
The statement rick made "flirting with disaster" is very true. If you consider the replacement inconveinent, then how about having fire apparatus or ambulances parked in your yard?
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Electrical entrance cable
[ 7 Answers ]
We have been advised by our insurance co. to replace the electrical entrance cable... does anyone know exactly what that takes... what materials,etc... thanks..
Service entrance cable
[ 23 Answers ]
I am re-wiring an old house. It is a small 2 bedroom, 1 bath house. We put in a 200 amp service and need to run a service entrance cable about 20 -25 ft to the inside breaker panel. My question is how big of a gauge wire should we run for the service entance cable. #? 3 conductor with ground in...
Service entrance cable
[ 2 Answers ]
Having new 100amp meter installed professionally,but I am burying wire to the building which is 125' from where meter is mounted. Will I have to upsize the size of wire because of the distance? I also intend to enclose in conduit, so I'm not worried about using "U" coded wire
Entrance Cable
[ 4 Answers ]
I am putting in a new electric service in my house and wanted to know what size wire I need for a 200 amp service
Service entrance
[ 5 Answers ]
Can someone tell me how to find out what the amp rating of a service to a house is . The fuse box is old with edison base fuses, but the weather head and pipe to the meter cradel looks newer want to change to beaker panel
Not sure what size
View more questions
Search
|