Baseboard Heater Wiring?
Hi, I'm hoping someone can confirm I'm on the right track so I don't burn our house down :)
I'm installing a 240V Baseboard heater. It's the only heater that will be on this circuit & I actually haven't bought it yet but I intend to buy a 1500W (or less) baseboard for a 12' x 12' bedroom. I have a role of 14/2 wire & know that 14/2 is code for a 110V 15A circuit... can I use the 14/2 for 240 as well with a 15A 2 pole breaker?
I was looking at the other baseboard heaters in the house & they are 12/2 but there's several heaters in series totaling more than 15A?
Just thought I better ask before making a mistake.
Happy Holidays!
Marty
|
|
 |
Uber Member
|
|
Dec 28, 2008, 11:41 PM
|
|
For your example you have to take 1500W * 1.25/240 V and size up to the next available breaker size, so a 15 A, 14/2 wire is OK.
The 1.25 is a derating factor that's necessary for heating loads.
|
|
 |
Full Member
|
|
Dec 29, 2008, 02:47 PM
|
|
Be sure to put some black tape on the white wire to re-identify it as an ungrounded conductor.
|
|
 |
Junior Member
|
|
Dec 29, 2008, 03:46 PM
|
|
Marty, Don't forget to buy a thermostat, DPST with an 'OFF' position.
|
|
 |
New Member
|
|
Dec 30, 2008, 12:59 AM
|
|
 Originally Posted by benaround
Marty, Don't forget to buy a thermostat, DPST with an 'OFF' position.
Hi Ben... what's the purpose of such a thermostat? I figured on buying a regular inline thermostat that turns the heater on & off whenever it gets below 60 or 70 or whatever it's set at. What's the purpose of the off setting?
Thanks for all the tips guys.
Marty
|
|
 |
Uber Member
|
|
Dec 30, 2008, 08:38 AM
|
|
That stat uses an SPST switch to switch on heg of the AC when it's controlling. When you move the stat to off the other leg is turned off so you can safely work on the heater.
In Case #1, if there was a heater break the ends can have anywhere from 0-120 V with respect to ground when supposedly "off". The later makes the heater elements safe.
People expect OFF to mean OFF, although it's not always the case.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Baseboard Heater Wiring
[ 20 Answers ]
Hello, after reading quite a bit I thought I had this wrapped up but I guess I don't. I am trying to wire up some baseboard heaters for the garage. I have run a 12/2 from the panel on a 20 amp double pole breaker which goes to a double pole t-stat (I want to be able to completely shut off the...
Wiring baseboard heater
[ 1 Answers ]
Can I run hot 220v to either end of heater and wall mounted tstat double pull to either end?
Wiring for baseboard heater
[ 1 Answers ]
I need help wiring my downstairs with baseboard heaters. First Heater: I have the main power supply and wire from the thermostat coming in. I then have a wire running from my first heater to the second heater. The heaters are 220-volt. What wires do I connect in order to complete the circuit?
Baseboard heater wiring
[ 1 Answers ]
I have 3 separate 12-2 cables going into the thermostat box each cable contains a black, red and a ground. One of the wire comes from the power supply and the other 2 wires are for 2 separate baseboard.
My thermostat is a Honeywell RLV340. It has two black wires.
How should I wire these...
Baseboard heater wiring
[ 3 Answers ]
Hi All,
I have a question about wiring my base board heaters.
I am currently re-wiring my basement, adding a few heaters on the original 240V-20A circuit.
It will be handling a total of 3500 W, no problem.
The question is about the wiring itself, here's what I intend to do:
Run from...
View more questions
Search
|