    Sizing of UPS
    Dual UPS should be used to drive Server and networking equipment load. Both UPS should share load equally in normal operation. But during maintenance or any break-down of one UPS other UPS should be able to take total load. Server will remain on always.
    What should be rating of single UPS in terms of kVA if the total load is 95kW ? Or what is criteria for selection of appropriate rating of UPS for a given load ( Say 95kW)?

    Thank you.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Dec 28, 2008, 05:53 AM
    To convert KW to KVA, one method requires the Power Factor of the load be known, as:

    KVA=KW/PF,

    Or, if you know the total amps per phase, then:

    KVA= Amps x Volts / 1000, for single phase, or,
    KVA= Amps x (Volts x 1.73) / 1000 for 3 phase.

    Assuming a 208 volt 3 phase system, with a 90 PF of the load, then:

    KVA= 95/.90
    KVA=105.56

    Or, assuming 275 amps per phase at 208 volts 3 phase, then,

    KVA= 275 x (208 x 1.73) / 1000 = 98.956

    I recommend a system this size be 3 phase if at all possible.

    This will arrive at the minimum size of each UPS, since each UPS will need to assume all load during a Maintenance Window.

    The UPS system should be static sized larger for any additional future load, or be scalable.

    I suggest you consult with MGE, Liebert, or Powerware, for advice on a system this size.

    If you need to consider Tier Certification, consult with The Uptime Institute - Improving data center uptime and the world’s IT productivity through benchmarking and collaborative learning..

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire sizing and conduit sizing [ 8 Answers ]

I am looking for confirmation on some of the info I have found and answers to a few missing pieces. This is regarding wire size and conduit size for service conductors from the meter to the breaker panel (about 30 ft away). Wire Size: 125A service needs #2 copper or 1/0 aluminum -- #6 copper...

Ductwork sizing [ 1 Answers ]

I'm trying to extend ac ductwork to a storeroom. Here is where I am: 3 1/2 ton ac, air handler to 14x22 plenum to 3 branches (small) & to a 12 foot long insulated 10" x 10" main branch with 3 small registers to a 10 foot long insulated 6" x 6" branch with two small registers to a cement block...

Sizing of UPS [ 2 Answers ]

Hi, If I have 300 computors each with a load of 400watts and I want to make provision for UPS back-up, what size UPS do I cater for? I have 3 phase 400VAC available.:rolleyes:

Bow Sizing [ 2 Answers ]

How does one determine what size bow to buy? I have noticed many lengths and draw distances. I don't want to spend a lot of money on a bow to find out it is not comfortable to use.

Sizing the kva for TRANSFORMERS [ 2 Answers ]

What Would Be The Right Size Transformer. Power Coming In Would Be Single Phase 480 Output Is 120v , About 4.2a I Figure About 1kva Would Be Plenty


View more questions Search