    Heater keeps blowing fuse
    Help York heat and air keeps blowing fuse. Connected diret bypass fuse blower motor will run but no heat.
    letmetellu's Avatar
    letmetellu Posts: 3,151, Reputation: 317
    Ultra Member
     
    #2

    Dec 23, 2008, 07:32 PM

    What fuse are you talking about? Is it a little 3 amp fuse on the circuit board of the furnace. If that is the one then you have a problem with the low voltage wiring. It could be a small wire that has rubbed into the metal of the furnace or it could be two wires touching somewhere in the low voltage wiring.

    If it is the 3 amp fuse do not jumper across it or you can possibily burn up the board or gas valve and change a small problem into a big one.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #3

    Dec 23, 2008, 07:57 PM

    Or is it the fuse in the ssu switch located outside the furnace?
    gradeset's Avatar
    gradeset Posts: 7, Reputation: 1
    New Member
     
    #4

    Dec 26, 2008, 05:10 PM
    Sorry new to this. The fuse is a 8 amp that is located on the ssu switch. We replaced the capacitor and that guess didn't work. So now looking for some real help.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Dec 26, 2008, 06:25 PM
    The SSu switch has a on off switch and a fuse I assume. If you bypass the fuse on a temporary basis you said the blower motor ran? When you turn the thermostat up does the burner come on at all?

    Post the exact model number for the York unit.
    gradeset's Avatar
    gradeset Posts: 7, Reputation: 1
    New Member
     
    #6

    Dec 27, 2008, 09:40 AM
    Quote Originally Posted by hvac1000 View Post
    The SSu switch has a on off switch and a fuse I assume. If you bypass the fuse on a temporary basis you said the blower motor ran? When you turn the thermostat up does the burner come on at all?

    Post the exact model number for the York unit.
    When we bypassed the ssu switch and fuse the burner came on. Breaker tripped before fan could come on. There is no on off switch on ssu just a plug in for the heater and a spot for the 8 amp fuse. I am assuming its called a ssu switch? The heater is a york diamond 80 about 5 years old. Thanks for any help.
    MarkwithaK's Avatar
    MarkwithaK Posts: 955, Reputation: 107
    Senior Member
     
    #7

    Dec 27, 2008, 10:11 AM

    Sounds as if your blower motor has shorted to ground, either internally or somewhere along the external wiring connections.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #8

    Dec 27, 2008, 10:16 AM
    I agree I would check out the blower motor first.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #9

    Dec 28, 2008, 04:33 PM

    Yep, definitely sounds like blower motor or motor wiring, most likely will need new motor.
    gradeset's Avatar
    gradeset Posts: 7, Reputation: 1
    New Member
     
    #10

    Jan 18, 2009, 08:22 PM

    Hello again, well I finally was able to get a tech to come out and look at my heater. This is what happened he plugged the unit in bypassing the fuse and it worked great.So he then plugged unit into the fuse switch and is still running. I have no idea what happened but thanks for all help given.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #11

    Jan 18, 2009, 11:23 PM
    Strange indeed.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Nordyne heater fuse keeps blowing. [ 1 Answers ]

Problem: The 3 amp fuse on the circuit board keeps blowing out Symptoms: The red led light is on continuously. History: The fuse was blown before, but the guy who installed the unit found a short outside that was causing it. Now it appears to be something different. Question: "False flame or gas...

Ecu fuse blowing [ 3 Answers ]

When try to start 91 Crx, ECU fuse blows. Had another Ecu for dual injectors. Car started. Replaced ecu for 4 injectors fuse blew again. HELP!! :confused:

ACG (ALT) (S) fuse keeps blowing [ 12 Answers ]

Hi all I found this site as there are a few of you who have run into this problem but mine is slightly different. The ACG (ALT) (S) fuse keeps blowing in my civic e.g. hatch after a d16z6 swap. The swap was from carb to fuel injection and I kept the original tank (which had no internal fuel pum)...

Fuse keep blowing [ 1 Answers ]

I am not sure what is happening, We have two units the upstairs is running just fine. Now the downstairs keep blowing the fuse in the furnace. What it does is that it will let the fan run but when I reduce the temp. so the a/c will come on it blow the fuse. Thanks, George

24V fuse keeps blowing [ 1 Answers ]

HI all, I have a problem with my AC it keep blowing the 3amp fuse I have replaced it but after a min or 2 it blows again I have measured the transformer Volt. To be at 27.8V I know it's a 24V tramsformer now could this be why its blowing the fuse or it doesn't really matter that its 3V over... ...


View more questions Search