New Member
|
|
Dec 17, 2008, 04:01 PM
|
|
Day and night package unit won't shut off
Imo new at this service and I can't get a hold of my super. Please help!! Unit called for heat furnaces fire off and when the room is satisfied burners shut down and the blower keeps running. I checked the role out, hi limit, safety at the blower and even changed the circuit board. Is there anything else to check?
|
|
 |
Ultra Member
|
|
Dec 17, 2008, 04:08 PM
|
|
Thermostat fan selector switch- set to on or auto? Maybe a stuck time-delay stack switch-give the unit a good thump near the control compartment, see if blower stops.
|
|
 |
New Member
|
|
Dec 17, 2008, 04:16 PM
|
|
I even disconnected the red and green at the t-stat... even gave the relays a good thump.
|
|
 |
Heating & Air Conditioning Expert
|
|
Dec 17, 2008, 04:46 PM
|
|
Stuck blower relay of some sort
|
|
 |
New Member
|
|
Dec 17, 2008, 04:56 PM
|
|
Can u elaborate a little more if possible
|
|
 |
Heating & Air Conditioning Expert
|
|
Dec 17, 2008, 05:22 PM
|
|
Sure. Trace down the blower relay in the furnace circuit. Then test the relay to see if the contacts are welded shut causing the blower to run all the time.
You might also check for a shorted thermostat wire causing G to be activated all the time. Test by removing the G=Green wire off the circuit board terminal and see if the blower keeps running.
|
|
 |
New Member
|
|
Dec 17, 2008, 06:23 PM
|
|
If I remove all t stat wires from the board and the blower keeps running then is that 100 percent that the circuit board with the relay is bad?
|
|
 |
Ultra Member
|
|
Dec 17, 2008, 06:40 PM
|
|
Find the part number from the circuit board. It might start with "HH84AA..."-
|
|
 |
Ultra Member
|
|
Dec 17, 2008, 08:28 PM
|
|
If the transformer is bad on this furnace the blower will run until the power is shut off.
So do you get any response when you turn the fan to the on position or if you turn the A C on, if not still a indication that the transformer is bad.
|
|
 |
Ultra Member
|
|
Dec 17, 2008, 08:37 PM
|
|
 Originally Posted by pauly2121
Imo new at this service and i can't get a hold of my super. please help!!! unit called for heat furnaces fire off and when the room is satisfied burners shut down and the blower keeps running. i checked the role out, hi limit, safety at the blower and even changed the circuit board. is there anything else to check?
If the heating still works, the transformer must be OK. Some of these units use a normally closed relay for blower control, and the relay is powered to turn the blower off. Failure of the timing circuit on certain boards will result in continuous fan, while the other control functions of the board are maintained. Did you replace the board with new or used?
|
|
 |
New Member
|
|
Dec 10, 2012, 10:47 PM
|
|
With thermostat wires off \ disconnected from circuit board take a volt meter and test between red and white - if you get 24 volt reading heat is off and you have stuck relay in circuit board. If you get a reading of 0 volts with t stat wires off circuit board then change board that's the only option to make it work. Once you pull off circuit board look at back side for burnt spots- look front side for burnt diaods and browning around circuits - this is just for you own info
|
|
 |
Uber Member
|
|
Dec 11, 2012, 02:13 AM
|
|
L
 Originally Posted by altonbee
with thermostat wires off \ disconnected from circuit board take a volt meter and test between red and white - if you get 24 volt reading heat is off and you have stuck relay in circuit board. If you get a reading of 0 volts with t stat wires off circuit board then change board thats the only option to make it work. Once you pull off circuit board look at back side for burnt spots- look front side for burnt diaods and browning around circuits - this is just for you own info
This post is 4 years old! Look at the original posting date. But, thanks for helping.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Frigidair package unit not heating up, blower always on
[ 41 Answers ]
Hi all, I have a Frigidaire package unit heater/air conditioner and my heat does not work suddenly. All was fine until the night before thanksgiving I came home and the house was down to 63 degrees and the vents were blowing cold air!! The model number of my unit is R4GA-036K072C and apparently it...
Outside a'c unit won't shut off
[ 2 Answers ]
My A/c Unit Out Side Won't Turn Off When The Thermostat Inside Is Turned Off.there Is Also Ice On The Lines Outside.I Have A Dual A/c System, One For Each Side Of The House. I Turned Off The Main A'c Switch ,the Fan Stopped And I Heard A Click, I Waited 1 Min. And Turned It Back On Again And Heard...
Inside unit won't shut off
[ 1 Answers ]
My ac unit sometimes goes off outside but stays running inside . I have to throw the breaker to make it go off . Is it my thermostat or something else ?
Trane package unit
[ 5 Answers ]
Hi all I'm having a problem with a unit runs good ,cools good, unit will run fine then just shut off ck unit giving no codes reset unit it runs fine until it just shuts off again
Anybody Know Anything About A Package Unit
[ 2 Answers ]
My Mother just had a Trane 15 seer Package unit installed. She told me she was having some problems with it and asked if I would come and look at it. The installer was acting very professional. This is the problem. The condensation line comes out and makes a 90 degree turn and runs about 3 feet....
View more questions
Search
|