Carrier 38EYG060300 heat pump
Hi Folks,
I have a fairly basic question about the proper function of my heat pump (heat cycle).
During warmer weather 45F and above the unit comes on and heats seemingly OK. Once the temp has dropped below 45F or so then it seems my gas on the inside furnace runs much more and the heat pump does not come on. Is this normal operation or should I be expecting the heat pump to give me heat below 45F? Earlier in the summer the air conditioning had quit, we had a company out and they replaced a small valve which fixed the air conditiong but I am now concerned why the gas is on so much on the furnace.
Things I do know is that there is a thermostat outside that shows me the outside air temperature. Am I concerned about nothing? I thought heat pumps worked even in cold weather?
Appreciate your help.
Smtx
|
|
 |
Full Member
|
|
Dec 15, 2008, 08:39 AM
|
|
At 45F your unit should be able to provide most or all your heating needs, unless the unit is grossly undersized (which I doubt). My aging 18 year old York was providing all my heating needs this morning with 40F outdoor temps. I even have the furnace locked out above 40F to keep the wifey from impatiently demand being warm right now!
A number of things come to mind that might be wrong: refrigerant leak, bad control module/board in heat pump, bad tstat, etc.
|
|
 |
New Member
|
|
Dec 15, 2008, 09:10 AM
|
|
Dac122,
Thanks for your input, I thought so, just seems my aux heat is on at too high a tempurature. I suppose the cut-over is set a little to high. I mean to say the aux seems to come on too soon. IE around 43F and I don't see the heat pump come on below this.
I suppose the fine-tune parameter is where gas cost more than electric KWH to run the heat pump. But my hunch is that the heat pump is still cheaper to run to a certain point.
smtx123
|
|
 |
Full Member
|
|
Dec 15, 2008, 09:17 AM
|
|
Depending on the performance of your heat pump (Coefficient of Performance Curve), your electric and gas rates, a heat pump can be more cost effective to run than your furnace down to a certain temp. We call that the economic balance point.
Once you figure out what's wrong and get it addressed, go repost and we can fine tune where your HP should cut out and furnace take over to maximize your savings.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Carrier Heat Pump
[ 1 Answers ]
I have a 4 ton Carrier Heat Pump Heating and AC unit. Lately, the unit has been making a horrendous, loud bass trombone sound. This sound comes from the outside unit that houses the fan and compressor. It occurs when the heater/blower in the atic is NOT on. The sound is so loud that it wakes me up...
Carrier heat pump
[ 14 Answers ]
I Have A Carrier Heat Pump Moel #38ycb036300 That Was Working Fine Yesterday. Today It Will Not Come On. Thermostat Is Okay. What Should I Look For, Is Their Any Problem Parts In Extreme Heat? I Used It On And Off For The Last Two Days After A Six Month Rest. Minor Usage For The Heat This Winter....
Carrier heat pump
[ 1 Answers ]
Hi,
How can you tell how old the unit is by the model or serial number?
Serial is #3996e24342, model # is 38ycb03030300.
Thanks!!
spence
Carrier Heat Pump
[ 2 Answers ]
I have a 4 ton Carrier Heat Pump Heating and AC unit. Lately, the unit has been making a horrendous, loud bass trombone sound. This sound comes from the outside unit that houses the fan and compressor. It occurs when the heater/blower in the atic is NOT on. The sound is so loud that it wakes me up...
Carrier Heat Pump
[ 1 Answers ]
Carrier Heat pump does not come on. Just stopped working. How do I trouble shoot for a bad transformer or other parts related to unit no turning on for either a/c or heat?
View more questions
Search
|