    Rheem Control Parts
    Can someone tell me the purpose of the following limit switches?

    - main limit control
    - rollout control
    - vent safety control

    Granted they measure overtemperature. It appears one looks for over temp of the air duct venting into the house, one looks for overtemp of the exhaust duct, and one looks for overtemp in the vicinity of the burner. Can someone confirm or correct. And which one is which?

    From the schematic, all of these appear to be normally closed and on the same control loop. The induced draft and indoor blower motors would come on but the burner would not. I jumpered out the control loop to see if the burner would light, and it did, so I think I have one of the aforementioned sensors that is bad, but I haven't taken the time to figure out which one, so I thought I might just replace them all depending on cost. If expensive, I'll have to find my volt meter to troubleshoot. But they seem to be simple thermostat type devices - I'm assuming they can be found for a couple dollars each. Or perhaps replace them with similar open on rise button thermostat type devices. But I don't know the temperature specs or the ramifications.

    The schematic also says two of the switches are "manual reset". How are they reset?

    Where can I go, either online or storefront, for replacements for the above limit switches along with negative pressure control switch?

    I replaced the thermocouple last year, purchasing the replacement at HomeDepot but they don't appear to carry the above items.

    While I'm at it, where can I get the replacement Honeywell gas valve?

    Thanks in advance.
    sunset_atl's Avatar
    sunset_atl Posts: 2, Reputation: 1
    New Member
     
    #2

    Dec 13, 2008, 12:36 AM

    By the way, the model is a Rheem, RGDG 075AVER

    Thanks again.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #3

    Dec 13, 2008, 11:53 AM

    The main limit control is typically an auto-reset type and senses temperature near the heat exchanger. Poor airflow will trigger this one. The vent safety control can be either manual or auto reset and senses exhaust/inducer housing temperature. A restricted secondary heat exchanger will trigger this one. The roll-out limit is almost always a manual reset type, senses temperature in the burner vestibule area, and if it trips open you probably have a failed primary heat exchanger. You will likely require the services of a professional for anything beyond the main limit scenario.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Evaporative Emission Control System Purge Control Valve circuit Malfunction [ 3 Answers ]

p0443 Evaporative Emission Control System Purge Control Valve circuit Malfunction on mazda melinia s 1996 83k?what is the next stip? I cleared the check engine light and it went off ,and after 60miles driving it cames back again?why and how can I fix it ? Also what is the cheapest way to reset...

Rheem Furnace Fan Control Center Transformer [ 2 Answers ]

I was replacing my transformer/fan control center for a Rheem Furnace (central Heat/air) and did not label the wires. I am now very confused... I have two sets of contact wires coming out of the relay, one set "no" and the other "nc". And the Primary wires on the transformer... How do I connect...

Rheem heat pump rpka-030jaz fan control [ 5 Answers ]

What controls the fan on my heat pump? It's running all the time, whether the compressor is running or not, and I can't tell from the diagram on the back of the shroud what actually tells the fan to shut off when temp is reached and the thermostat shuts down the compressor.

Rheem furnace old fan control wiring [ 5 Answers ]

Does anyone know where I could obtain wiring schematic for an old Rheem furnace built in 1976?


View more questions Search