    Quick Cycling
    Janitrol GDT 090 4A will ignite on first cycle, then burn 1-5 minutes, then cycle to blower for several minutes, then try to ignite again, sometimes it gets a minute of burn time, but mostly won't even get to ignite. Eventually cycles until I reset, then starts the whole process over again.

    Sometimes, it will actually cycle properly for a few hours.

    LED initially indicated open pressure switch and open limit. Replaced both (including aux limit) as well as new flame sensor. Now I still get both signals, along with open flame sensor, but only intermittently. Mostly it just cycles.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #2

    Dec 12, 2008, 03:09 PM

    Check the ground wire to the ignition control/circuit board. If the connection is poor it will produce the same fault code as a dirty sensor. If you are still getting the high limit fault code, then you still haven't corrected the condition that is making the furnace overheat. More than likely, you have an airflow restriction somewhere in the system. You can replace the limit control every day and it won't correct the problem.
    chazzone's Avatar
    chazzone Posts: 3, Reputation: 1
    New Member
     
    #3

    Dec 12, 2008, 03:22 PM
    Quote Originally Posted by KC13 View Post
    Check the ground wire to the ignition control/circuit board. If the connection is poor it will produce the same fault code as a dirty sensor. If you are still getting the high limit fault code, then you still haven't corrected the condition that is making the furnace overheat. More than likely, you have an airflow restriction somewhere in the system. You can replace the limit control every day and it won't correct the problem.
    Thanks, but the system isn't getting hot enough to over heat, after the first burn, and I get the same open limit code even when it is cold after running for minutes or hours without ignition.

    I have replaced the filter and cleaned the AC coil in the bottom of the unit. I even let it run with the upper access open and no filter, and the bottom access open, so I could make sure it wasn't an air restriction issue.

    I'll recheck the ground, but everything there is clean and appears to be all right.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #4

    Dec 12, 2008, 06:20 PM

    Odd, to get so many fault codes at the same time... check the multi-connector plugs at the circuit board-unplug and reconnect them several times to "scrub off" the pins and sockets. Also check board for evidence of moisture exposure and/or oxide bridging of the circuit paths.
    chazzone's Avatar
    chazzone Posts: 3, Reputation: 1
    New Member
     
    #5

    Dec 13, 2008, 12:21 AM

    I'll do that, but right now it seems to be running like it should, and I hate to provoke it with the temps in the low teens.

    I did look at the board prior, and although I saw some dark areas on the back of the circuit board, there was no real sign of damage.

    I considered that this might be the problem (considering the lack of an obvious cause), but at more than $100, I'd rather cover my bases first.

    Thanks for your help
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #6

    Dec 13, 2008, 11:33 AM

    Dark areas on the board? A sign that you may be headed toward a dark place... if the problem returns take a closer look.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

AC unit is quick cycling [ 1 Answers ]

My ac unit is cycling on and off quickly. Sometimes in 30 seconds to 1 minute intervals. Also the digital thermostat goes blank during the quick cycling. Could this problem be caused by a faulty thermostat. Thanks in advance for your help.

Bryant AC blower fan motor "quick" cycling [ 11 Answers ]

While running in AC mode or fan ON mode the blower fan keeps cycling on/off contiuously for on off periods from less than a second to several minutes. I figured the motor was overheated (bad windings) so I replaced the motor and capacitor with poor results. It seems to run longer but contiues to...

A/c cycling too often [ 3 Answers ]

Just installd a honeywell thermostat (rth230b) it run until it reaches the set temp. then it shut off then it comes right back on within seconds. Please give some advice on what could be problem. Thanks

Altima Turn Signal Quick cycling [ 1 Answers ]

I have 1999 Altima which the passager side turn signal bulb appears to need replacing.. (Quick cycling). How do I replace the lamps? Do I have to remove the front headlight to get access? Thanks:cool:

Fan Keeps Cycling [ 1 Answers ]

I have a Carrier central A/C and a Propane FAG furnace in my basement. The problem is that after the A/C or furnace has shut off, the fans continue to cycle off and on just as if the A/C or furnace was still running.:mad: Sometimes the fans (there is 2 of them, I believe) run continuously and...


View more questions Search