    New thermostat wiring = no a/c
    I am switching my totaline therm with a honeywell basic thermostat... when I rewired and put in the honeywell the electric heat works however the a/c handler does not even turn on and the fan does not run independently as it should have either system if I choose

    The previous wiring was set up as W O G R C Y with white - W, O had no wire, G - green, R - red, C - blue, Y - yellow

    On the new therm there was Rh, Rc, W on one side and Y, G on the other... I put red to Rh, blue to Rc, white to W and then yellow to Y and green to G

    Heat works and blows fine, nothing else happens when I turn on the air or the fan

    I have central air and electric systems on both... not sure if I just have a wire crossed or what
    dac122's Avatar
    dac122 Posts: 463, Reputation: 17
    Full Member
     
    #2

    Dec 12, 2008, 02:22 PM

    Looks like blue was your neutral common on the old tstat. I think you just need to switch that blue to your neutral common terminal on the new honeywell, and jumper the Rh and Rc together with a small wire. That should allow current to flow through to energize Y.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Dec 12, 2008, 04:10 PM

    Rc and Rh gets jumped together and becomes R and would then be connected to RED only.
    charonx3's Avatar
    charonx3 Posts: 2, Reputation: 1
    New Member
     
    #4

    Dec 12, 2008, 04:17 PM
    Quote Originally Posted by dac122 View Post
    Looks like blue was your neutral common on the old tstat. I think you just need to switch that blue to your neutral common terminal on the new honeywell, and jumper the Rh and Rc together with a small wire. That should allow current to flow thru to energize Y.


    Do I just tape off the blue wire if there's no other terminal and run the jumper
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #5

    Dec 12, 2008, 05:42 PM

    If the new t-stat does not require a "c" connection, do not use the blue wire-clip the bare end off & tape it.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring codes from old Carrier thermostat to new Hunter thermostat [ 1 Answers ]

WIRING CODE HELP FOR THERMOSTAT I am in an office and have an old Carrier programmable thermostat which no longer works. I purchased a Hunter 44660 thermostat to replace. My problem is that the wiring codes on the previous thermostat do not match up the codes on the new thermostat. Codes and...

Thermostat Wiring - From Two to One Thermostat [ 4 Answers ]

Currently my central a/c unit is hooked up to a Honeywell CT3500 Programmable Thermostat. I've noticed that the thermostat can handle heat as well as cooling. My furnace is hooked-up to an older manual thermostat. It is a simple 2 wire set-up - red & white. Could the furnace be hooked-up to the...

Wiring direction for a multi wiring system thermostat! [ 3 Answers ]

I have a 2 wire system (3 phase), need to connect multi wiring system thermostat! Need to know if, its correct to just use line#1, and the device already has a jumper?

Thermostat wiring [ 1 Answers ]

Hi, I have a 5-wire bundle coming out of my wall (red, blue, green, yellow, and white). These colors went to my old honeywell T8001C. Those terminals were labeled (G, C, R, W, Y). There were also letters B and O yet, these terminals were not being used. I purchased a new HUNTER 44860...

Honeywell wiring different from old thermostat wiring [ 2 Answers ]

I purchased a non-programmable digital thermostat to replace an analog thermostat with wiring red, white yellow and black. How do I match the wiring? HELP!!


View more questions Search