    220 baseboards low heat
    I have a 2000w baseboard on a double pole thermostat. It wasn't providing enough heat for the room size so I installed an additional 1500w on another wall. I wired it to the to the main baseboard opposite end from where it is wired to the thermostat with #12 with run of about 16'. They are both getting warm but not hot. What could be wrong?
    Thanks
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Dec 12, 2008, 12:44 PM
    Sounds like you wired both units in series. Needs to be wired in parallel.

    If you butted new heater next to an existing, and spliced wires together in both ends next to each other, that's what happened. Some how you need to get the feed cable supplying the other end of the existing to the new unit.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Electric baseboards [ 1 Answers ]

Where is the best location for installing electric baseboards ? On an exterior wall or interior ? Also is a unit mounted stat adequate or should I spend the extra and get wall mounted stats ? Thanks in advance. Chuck

Wallpaer & baseboards [ 1 Answers ]

Is it best to install wallpaper before or after installing baseboards?

Replacing baseboards [ 1 Answers ]

I have just purchased a new home and I'm refinishing all the rooms with new sheetrock, flooring etc. I would like to replace the baseboard heating because the fins are all bent up and the covers have many layers of paint on them. My question is how do I release the water from the system so I can...

No heat in bedroom baseboards [ 1 Answers ]

I installed a new Peerless hot water boiler. Have a single zone system which now provides plenty of heat to lower half of house, the upstairs bedrooms of this split level house has no heat. I installed a bleeder valve in one of the bedroom base boards and bled the system there until water started...


View more questions Search