Back to back WC drain fittings
How do I plumb back to back WCs? The IRC restricts the use of a double sanitary T for WCs. Is there another combination of fittings that are acceptable such as a double Y? I will have 10" floor joists and a 2x6 wall between the 2 WCs.
The IRC does allow the double sanitary T if the "horizontal developed length between the outlet of the water closet and the connection to the double sanitary tee is 18 inches or greater." Is the 18" measured from the center line of the WC flange to the center line of the stack or is it measured between the hub of the T to the hub of the elbow on the WC?
|
|
 |
Plumbing Expert
|
|
Dec 7, 2008, 11:43 AM
|
|
Yes, you can use Double Y. It is commonly used in back-to-back wc installations. See image...
|
|
 |
Senior Plumbing Expert
|
|
Dec 7, 2008, 01:30 PM
|
|
Milo...
That isn't any double wye I know of... That is a double combination wye 1/8th fitting. I can, however see how an inspector would allow this fitting!
Moosehead, if you want the toilets directly back to back with a 2"x6" wall between them then you cannot satisfy the 18" rule you mentioned.
See if your inspector will allow the double combination wye 1/8th fitting... let us know will you.
Thanks...
MARK
|
|
 |
Plumbing Expert
|
|
Dec 7, 2008, 01:55 PM
|
|
Mark, that's exactly what I was trying to say...
In my area, some inspectors ask for dbl Y because in case of cloggage, snake will not travel across to the opposite toilet but will be guided downwards...
|
|
 |
Senior Plumbing Expert
|
|
Dec 7, 2008, 02:01 PM
|
|
I hear you Milo... same here, but that fitting you posted isn't a double wye... that's all I was saying... ;)
Hey, can I PM you with another issue I need help with?
Let me know... ok?
Thank you.
|
|
 |
Plumbing Expert
|
|
Dec 7, 2008, 02:17 PM
|
|
 Originally Posted by massplumber2008
I hear ya Milo...same here, but that fitting you posted isn't a double wye....that's all I was saying...;)
Hey, can I PM you with another issue I need help with??
Let me know...ok??
Thank you.
Sure, PM me... ( in the meantime, I have to figure out how to receive PM's... :eek: )
|
|
 |
Senior Plumbing Expert
|
|
Dec 7, 2008, 02:19 PM
|
|
At the very upper right of the screen/upper page there should be a private message icon under your name.
It will blink when you get a PM... I think... ;)
Writing now
|
|
 |
New Member
|
|
Dec 8, 2008, 04:40 PM
|
|
I will go to the inspector with the double combination Y 1/8 fitting and see what he says. Thanks for the quick replies.
|
|
 |
Senior Plumbing Expert
|
|
Dec 8, 2008, 04:41 PM
|
|
Let us know what he says...
Thanks...
MARK
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Back-Up During Drain Cycle
[ 2 Answers ]
During the drain cycle on my washing machine water overflows the line and comes out of my laundy box that I just had installed. The lines in the wall are 1 1/2 in diameter, I believe, but the standard box drain line is larger. The installer ran a line from the box about 30" down into the original...
Drain with back pressure
[ 6 Answers ]
I have a conventional sceptic system with two tanks - each serving one wing of my house.
My laundry room deep sink drain has pressure on it, enough to raise the water level in the sink about 10". This happens even when there is no water running down any drains connected to this wing - I even...
Shower drain back p
[ 2 Answers ]
Our lab suddenly started holding her head in the air sniffing . Very seriously sniffing. We were sitting in the family room with a 1/2 bath located off the family room. She kept holding her head in the air sniffing like we have never seen her do before.
My husband went into the bathroom and called...
Washing machine drain back up
[ 1 Answers ]
What can I do to clean out build up in drain lines. Evidently a snake will not work. Is there a chemical that will reduce or clean drain line build up?
View more questions
Search
|