 |
|
|
 |
New Member
|
|
Nov 29, 2008, 10:35 PM
|
|
GFI Outlets/Indoor Freezer
I'm trying to hang outdoor Christmas lights that shut down when sensing water, thanks to GFI breakers. Fine. Problem: a freezer hooked up to an inside outlet is also shut down. I cannot find a way to connect the freezer to any other outlets. Anyone have a solution?
|
|
 |
Electrical & Lighting Expert
|
|
Nov 30, 2008, 06:41 AM
|
|
No legal permanent solution.
You can temporarily move the freezer or run a cord to it from inside.
|
|
 |
Uber Member
|
|
Nov 30, 2008, 06:44 AM
|
|
A GFI breaker protects the entire circuit, as you have discovered. What you can do is remove the breaker and replace with a standard breaker, and install GFI receptacles where needed. You can use one GFI receptacle to protect standard outlets downstream, or just itself.By careful placement of GFI receptacles and allowing connection of either protecting or not protecting downstream, you can have both on a circuit.
If for example there are 3 outlets in the circuit before the freezer outlet, each would need to be a GFI device, and not protect anything downstream on the circuit, to allow non-GFI protection to the freezer. After the freezer, the next device can be a GFI and protect the remaining circuit.
If your not familiar with circuitry, this can be confusing. All depends on your abilities and knowledge. A qualified electrician can be called in and know how to trace out the circuit and install exactly what is needed.
If the circuit is for outlets required to be GFI protected, such as a garage or basement, the electrician should know that a receptacle for a stationary appliance, such as a freezer, can be non- GFI, but must be a single outlet, not a duplex.
|
|
 |
Electrical & Lighting Expert
|
|
Nov 30, 2008, 06:49 AM
|
|
Actually, TK's idea is much better.
I'm still half asleep. I hate waking up this late.
|
|
 |
New Member
|
|
Nov 30, 2008, 07:25 AM
|
|
Thanks to both of you for taking the time to help.
TKRussell's solution is a very good one, but for the few weeks a year that I run Christmas lights, I don't know that it is worth reconfiguring GFIs. The temporary solution-running the freezer to an indoor socket-occurred to me, but getting the cord through the door that runs from the garage to inside the house is a barrier.
Again, my thanks to you both!
|
|
 |
Uber Member
|
|
Nov 30, 2008, 07:40 AM
|
|
Whichever is easier for you. I, however, would never allow a freezer or refrigerator be GFI protected. Refrigeration compressors are popular for causing nuisance tripping, and if not noticed, loss of food.
Of course, when I install wiring, seems I end up owning any damage caused, so I need to be careful.
Since this is all yours, you may do as you like.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
GE icemaker in freezer is squirting water inside the freezer
[ 1 Answers ]
I have a GE side by side refrigerator with the ice and water in the door. My filter was clogged for about a week causing both the ice and water to stop working. A friend of mine came over and shook the ice bin quite violently trying to get the last bit of ice loosened up. A few days later we...
Amana bottom-freezer refrigerator: fridge not cold, freezer is frosty!
[ 1 Answers ]
Hi everyone!
I have a slightly over a year old Amana bottom-freezer refrigerator (model #: ABR1922FES).
Yesterday, I noticed that the fridge wasn't as cold as it should be, so I turned the temp control cooler, and then, as per the owner's manual, waited 24 hours for it to kick in. It didn't....
Maytag Side-by-Side Freezer ice buildup on floor of freezer
[ 1 Answers ]
I have a five year old Maytag side-by-side #MSD2754GR. I have had this problem for the last four years and have cleaned out the clogged drain plug each year myself. Seems that the ice buildup is coming somewhere else since water is not dripping down the back. Yes, it is humid and we are using...
Indoor pests
[ 1 Answers ]
We recently had a second sump pump installed in the ground level of our home. There has been a excessive amount of crickets. How do we rid of them so we can enjoy the family space on our lower level?
View more questions
Search
|