    Concord furnace start up after power outage
    Hi everyone, I have a 3 year old Concord model CG90UA. Having a problem re-lighting the pilot after a power outage. Have followed the procedure in the manual.
    The Honeywell controller is flashing an error code 4 flashes. This refers to a problem with the limit or rollout switch open?
    Have tried the procedure several times. Service is called but may not get here today.
    Any suggestions? They said this is a common problem but would not offer a solution over the phone.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Nov 25, 2008, 09:17 AM
    Find the limit and or rollout switch and see if it has a very small reset button in the center of the control. The back side of the blower door has a wiring diagram.
    canuk5838's Avatar
    canuk5838 Posts: 4, Reputation: 1
    New Member
     
    #3

    Nov 25, 2008, 10:10 AM
    Quote Originally Posted by hvac1000 View Post
    Find the limit and or rollout switch and see if it has a very small reset button in the center of the control. The back side of the blower door has a wiring diagram.
    Found both devices and there is no reset button. The limit switch is a round black plastic device and the rollout switch is a fiberboard with 2 leads. Removed it and there was no reset inside.
    Could this have something to do with the Honeywell controller? Can't find a number on it.
    canuk5838's Avatar
    canuk5838 Posts: 4, Reputation: 1
    New Member
     
    #4

    Nov 25, 2008, 10:38 AM
    Quote Originally Posted by canuk5838 View Post
    Found both devices and there is no reset button. The limit switch is a round black plastic device and the rollout switch is a fiberboard with 2 leads. Removed it and there was no reset inside.
    Could this have something to do with the Honeywell controller? Can't find a number on it.
    Found it SV9520.
    The product manual says
    4 flashes = "Limit string open.
    Combustion air blower is energized. If control
    system includes ST9160 Electronic Fan Timer,
    the heat speed circulating air fan will be
    energized until the limit string resets"

    Doesn't say how long this will take.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #5

    Nov 25, 2008, 12:17 PM

    It might take a couple of hours until it cools.
    canuk5838's Avatar
    canuk5838 Posts: 4, Reputation: 1
    New Member
     
    #6

    Dec 6, 2008, 12:03 PM
    It's taken awhile to respond with a thank you to those that offered help on this problem.
    I found the reset but it is not located at either device. It is up on the left side of the burner box. Learned two valuable lessons and would like to pass them along.
    1. location of reset as stated above.
    2. Root cause of the problem. When the tech arrived he showed me the reset and proceeded to restart the furnace. It would not star and the rollout switch tripped again.
    He then went outside. My furnace is vented via a horizontal black pipe which goes to the side of my home. There is an elbow with a screen on it. He removed the elbow and found the pipe was plugged up with wasp nests. After using a bar with a hook on the end, he removed the nests and reinstalled the elbow.
    The furnace restarted on the next try. No parts were needed but he did a complete inspection to insure everything was operating OK.
    THe whole ordeal cost $140.00 but maybe I can save someone a service call if this happens to them.
    My new fall maintenance plan is to make sure the filter is changed and check the exhaust vent to insure there are no obstructions.
    This is a common problem in SW Ontario.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #7

    Dec 6, 2008, 03:38 PM
    Glad you got it going,,
    MarkwithaK's Avatar
    MarkwithaK Posts: 955, Reputation: 107
    Senior Member
     
    #8

    Dec 6, 2008, 03:53 PM
    Quote Originally Posted by canuk5838 View Post
    This is a commom problem in SW Ontario.
    Not just SW Ontario. :(

    I've been on snow covered roofs shoveling out flue pipes here in NW Indiana.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Partial Power Outage [ 6 Answers ]

An amazing (to me) thing happened at our house yesterday. About mid morning, we started to notice several of our lights were out. Also, the stove had no power, but the fridge did. 3 of my GFCI circuits could not 'test' or reset at all indicative of no power. Several circuits were fine others...

Power Outage [ 4 Answers ]

The upstairs of my house consists of two rooms that are powered by two 20 amp breakers which are tied together. A few days ago one of the rooms lost all power while the other room continues to work fine. The power is still out and I have reset the breaker several times and this doesn't work. ...

Furnace blows cold air after power outage [ 1 Answers ]

My furnace made a loud noise as the power went out yesterday. The electricity is back on now, but the furnace only blows cold air? Is this something I can correct myself?

AC after power outage [ 2 Answers ]

After coming back from a family trip, we found that there had been a power outage. Several breakers were off position and some electronics (especially telephone) are completely dead. Now, after resetting the breakers, all the power problems are OK except AC. The control panel of AC seems...

Partial power outage [ 3 Answers ]

At Any Given Time The Power Will Go Out Only In The Living Room (outlets, Fans, Lights Etc.) And Also A Couple Of The Outlets In The Kitchen That Include The Refrigerator, Stove And 2 Add'l Outlets, All Others Work. Also The Ac Goes Out. The Rest Of The House Works. We Have A Devise That...


View more questions Search