    Heil High Efficiency locks out when weather is cold
    I have a Heil Model MULK125DK03 furnace. It works fine for AC and for heat as long as the outdoor temp is above 20 degrees. When it gets cold, especially when the temp is dropping the furnace intermittantly starts, gets to main flame and locks out with the ID fan running and nothing else. I come home to the stat calling for heat and the ID fan on.

    It happens very infrequently. I tried cleaning the temp sensor but no help. When it locks out it doesn't appear to try again.

    It fails when I really need it.

    Roger
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Nov 23, 2008, 05:51 PM
    If you have a two pipe plastic PVC exhaust system try disconnect the intake air pipe. Now DO NOT disconnect the exhaust of you will have a CO poisoning problem.

    The air coming into the furnace is about as cold as it is outside and can have a adverse effect on marginal electronic components. The units are designed to work with the combustion air coming from the outside but as parts get old they may loose the resistance to the cold temps and cause a problem. If this works it will get you out of the woods but not fix the problem.

    Use your head as this is only a test procedure I have used for many years since the new 90%+ furnaces hit the market. This will get you by until you can contact a dealer in your area for the repair or you can read this post from one of my earlier posts on this subject.

    .Your question is difficult to answer. It could be the small inducer motor or the capacitor for the inducer motor if so equiped the inducer might not want to spin at lower temps. Since it is temp related I would get a can of component freeze from Radio Shack. They use it on electronic circuits. You could spray it on some of the components when the unit is running and it might cause a shut down since you will be spraying a very cold product recreating cold conditions that the unit does not like to run in.

    There are other items that can cause this problem but this may help out.
    Hope this info helps.
    maggiesdad's Avatar
    maggiesdad Posts: 11, Reputation: 1
    New Member
     
    #3

    Nov 24, 2008, 05:13 AM
    HVAC1000
    Unfortunately I do not have a two PVC system. Intake air is from the room. My next step is the "shotgun" approach. I'll put a new temp sensor first, and then the electronic ignition module.

    Thanks for the help.


    Quote Originally Posted by hvac1000 View Post
    If you have a two pipe plastic PVC exhaust system try disconnect the intake air pipe. Now DO NOT disconnect the exhaust of you will have a CO poisoning problem.

    The air coming into the furnace is about as cold as it is outside and can have a adverse effect on marginal electronic components. The units are designed to work with the combustion air coming from the outside but as parts get old they may loose the resistance to the cold temps and cause a problem. If this works it will get you out of the woods but not fix the problem.

    Use your head as this is only a test procedure I have used for many years since the new 90%+ furnaces hit the market. This will get you by until you can contact a dealer in your area for the repair or you can read this post from one of my earlier posts on this subject.

    .Your question is difficult to answer. It could be the small inducer motor or the capacitor for the inducer motor if so equiped the inducer might not want to spin at lower temps. Since it is temp related I would get a can of component freeze from Radio Shack. They use it on electronic circuits. You could spray it on some of the components when the unit is running and it might cause a shut down since you will be spraying a very cold product recreating cold conditions that the unit does not like to run in.

    There are other items that can cause this problem but this may help out.
    Hope this info helps.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Nov 24, 2008, 05:23 AM
    The freeze component spray works I have used it many times in the past to find problems. I could not locate your model number so I did not know how your system actually operated or was hooked up..
    maggiesdad's Avatar
    maggiesdad Posts: 11, Reputation: 1
    New Member
     
    #5

    Nov 24, 2008, 05:26 PM

    I'll give it a try but the only thing that sees cold would be the gas line since the intake air comes from the basement. I guess that could cool the gas valve to the point of something sticking in it. I'll try cooling the gas valve.
    maggiesdad's Avatar
    maggiesdad Posts: 11, Reputation: 1
    New Member
     
    #6

    Dec 1, 2008, 06:29 PM
    Quote Originally Posted by hvac1000 View Post
    The freeze component spray works I have used it many times in the past to find problems. I could not locate your model number so I did not know how your system actually operated or was hooked up..

    I'll try the cool spray. I mistyped the model number. It is a NULK125DK03 made by Heil. I'm going to order a flame sensor and try it. From other posts it seems like the most likely to be tempremental. I found one fairly cheap from Keith Specialty.
    The temp locally went from 32 this morning to 24 when I got home from work to a house at 63 degrees, ID fan running, and thermostat calling for heat set at 68. It had worked fine all weekend with temps in the lower 30s. Thanks for your help.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #7

    Dec 2, 2008, 02:07 AM
    Post back with results

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Concord 90 Plus High Efficiency Heater [ 4 Answers ]

Can someone help me figure out why the fuse on my heater keeps blowing? I'm actually trying to run the air conditioner and get nothing, no fan or anything. I took off the front cover and found a #5 fuse on a small square panel/board. I change it and it just blows right away. Again it's a Concord 90...

Concord 90 Plus High Efficiency Furnace [ 2 Answers ]

If my hubby is correct, our central air also is "powered" by our furnace. For some reason, the air conditioning isn't working right. If you leave it on for more than an hour, it freezes up the lines going to the unit outside and only brings down the temp in the house by one degree! He cleaned it...

High Efficiency 5000 not cooling [ 2 Answers ]

I have a high efficiency 5000 central air conditioning unit that is not cooling, it is running but the air is not cool. It is model CA5536UKA1 serial LP31232822 Date of unit 3/1993. Could someone tell me what to look for or if it is low on freon.

Humidifier and high efficiency furnace [ 2 Answers ]

I have 7 years old high efficiency furnace and new flow through humidifier. Problem is that I do not have necessary level of humidity in my house. It is never more then 26%, which is dry. Should be between 40-60%. Everything works fine, water flows through humidifier every time furnace...


View more questions Search