    Cool air coming out of register vents
    Hello, I moved into this home late spring. I live in Ohio. From what I can tell and have research... there is a Goodman air exchanger with a downflow. There is not an airconditioner at all. There is a heating element built in because there are coils that turn on. So I haven't had any issues.. however it has been very cold... down to single digits at night and when I wake up the temperature is 61 degrees even though I have the thermostat set to 68. The temperature of the home never gets to 68 all day and the furnace runs constantly. Now here is the weird part. I can pull up the flashing around the furnace and feel the air it is putting out... it is warm... probably like 80 degrees or so. And if I feel the air coming out of a few of the vents it is warm... however it is cool coming out of most of the vents. And there isn't much air coming out at all upstairs... The unit is a Goodman ARUF049-00A-1A. I know it isn't the thermostat... I did put a new one in that was heat pump appropriate because I did read that I needed that online. Any help would be greatly appreciated... I am cold... Thanks
    letmetellu's Avatar
    letmetellu Posts: 3,151, Reputation: 317
    Ultra Member
     
    #2

    Nov 23, 2008, 08:58 AM

    This is probably silly to ask but have you changed your filter?
    If your furnace is very old it is possible that you have a belt driven blower, if this is the case the belt can get loose and therefore slow down the air movement, or the adjustable pully may need adjusting.

    You mentioned that your air coming out where you pulled the flashing away was about 80 degrees, that is too cool, it should be up in the 110 to 125 if it is an electric heat and it should be 135 to 145 if gas heat.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Furnace blowing cool air through vents [ 5 Answers ]

The other night my husband had turned the heat way up because he was cold. I turned it down because it was too hot. Ever since then I turn the thermostat up and select it to heat to 75 , but all the vents blow is cool air and the thermostat stays at 67 or 68 degrees. It is a programmable...

Furnace blows cool air through vents [ 1 Answers ]

Ignitors never ignite and the furnace never lights.. no burnt wires, the purge switch (negative switch) works, what could be the problem??

Air hardly coming through vents [ 1 Answers ]

Hi. I don't know much about furnaces but here is the problem as best I can describe. The air was on and worked fine. After awhile, the house got hot and I noticed that the air was barely moving through the vents. I would appreciate any advice I can get!

Water has invaded our register vents in slab house [ 1 Answers ]

We've just bought a 2 story slab house in September and after a big snow thaw & a couple inches of rain in the same time, all the register vents filled up with water. Luckily they did not overflow and we pumped it all out. We noticed a cracked tile in one vent, the rest are all metal--as we...

Cool Vents [ 8 Answers ]

I've just moved into a house in Albuquerque. We notice that the vents in the two baths actually blow "cool" air when the heat is on. Apparently, they are at the end of ducts. Is there anything that can be done to resolve this? Is there a pressure adjustment that is perhaps too low, or is the...


View more questions Search