    Blower speed
    Have a coleman model DGAAD56BDTA with the blower setting on high and I am just getting cool air, I know blue is low and red med. And black is high but where do I make the connection switch at, to put blue where black is ?
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #2

    Nov 20, 2008, 05:45 PM

    What does it say on the board where the blue red and black are connected? Does it say heat, cool, fan.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #3

    Nov 20, 2008, 05:47 PM
    Are you sure it's a fan speed issue, or is there possibly another problem. Does the furnace heat the house sufficeintly? Or are you having problems staying warm.
    raymondbl's Avatar
    raymondbl Posts: 3, Reputation: 1
    New Member
     
    #4

    Nov 20, 2008, 05:53 PM
    Quote Originally Posted by mygirlsdad77 View Post
    are you sure its a fan speed issue, or is there possibly another problem. Does the furnace heat the house sufficeintly? or are you having problems staying warm.
    Keep warm but just load and windy, has a reg. or transformer on bottom with red blue black and white, then red and blue jump to top, red is on cool blue on heat
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #5

    Nov 20, 2008, 06:15 PM

    Black should be on cool, normally red is on heat, but you say blue(lowest speed) is on heat, therefor you will not be able to lower the speed any further.


    Make sure all supply registers are open(if they are not, you will get too much flow from the ones that are, causing noise and draft) Also check filters. Good luck and please let me know how it turns out.

    Wouldn't mind if you rated my answer.
    raymondbl's Avatar
    raymondbl Posts: 3, Reputation: 1
    New Member
     
    #6

    Nov 20, 2008, 06:49 PM
    Quote Originally Posted by mygirlsdad77 View Post
    black should be on cool, normally red is on heat, but you say blue(lowest speed) is on heat, therefor you will not be able to lower the speed any further.


    Make sure all supply registers are open(if they are not, you will get too much flow from the ones that are, causing noise and draft) Also check filters. Good luck and please let me know how it turns out.

    wouldnt mind if you rated my answer.
    Yes the red is on heat and black goes to cool, out of the load transformer red goes to vac and blue to com, I never in 38 years had a furnace blow so hard, all vents are open fully, I think this would blow your hat off if you walked over a vent, has to be a blower control somewhere, thanks
    MarkwithaK's Avatar
    MarkwithaK Posts: 955, Reputation: 107
    Senior Member
     
    #7

    Nov 20, 2008, 06:56 PM

    DO NOT change the blower speed simply because you think it is loud. When changing the speed you have to take into account the heat rise across the exchanger (I think I'm starting to sound like a broken record). Too high and you will not get sufficient air transfer. Too low and your furnace can over-heat and go off on high limit and possibly cause irreversible damage to your heat exchanger. There is a balance and your furnace's nameplate will list the acceptable range.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Variable Speed vs. Single Speed Blower [ 1 Answers ]

Questions: Getting 2 new heat pump systems installed. 1.5 ton upstairs and 4 ton downstairs. Decided on Comfortmaker. Heat Load calc performed on sizes. Going 2 stage with variable speed downstairs with Honeywell IQ Pro stat. Was going to go one stage with variable speed upstairs with...

Furnace blower speed [ 1 Answers ]

Ihave a Goodman furnace with a variable blower speeds. I need to make the blower run faster for the A/C and slower for heat. How do I change the blower speeds?

Blower speed [ 1 Answers ]

How do I set the blower speed on a winchester furnace? Model number pcdfbld12n100a serial number ekgm366516.

Reducing blower speed [ 3 Answers ]

I have a Goodman ar60 airhandler with electric heat. The unit works great except that the blower is very noisy. The instructions say that I can reduce the RPM by switching the black wire with the red one on what looks to be a relay. There are 4 wires coming from the blower. White, brown,red and...

Blower Speed [ 1 Answers ]

I live in Las Vegas and my Electricity bill KILLS me in the summer months. I have talked with other people in my neighborhood with the same model home and my bill is double theirs. I tried to get the builder out here to look at my AC, and of course they do not respond. I am trying to find ways to...


View more questions Search