    Thermostat showing -AC when trying to start heater
    My heating systems was working up until yesterday morning. I smelt a gas leak in the garage near the hot water heaters. Had Atmos Gas come & check to verify and turn off gas. The plumbers came out and repaired the pipes that were leaking. The gas company came back out, turn the gas back on, relit all gas appliances and check the heating systems. When he tried starting the up stairs unit my thermostat would attempt to start the heater but show a -AC, blink the indicator lights, make a sound like some relays were trying to kick in, but it would never start. I swapped the top section of the thermostat with the one down stairs and both are working down stairs, but both are failing upstairs. What does -AC mean? Do you think the base electronics of the upstairs Thermostat has failed? Or could there be a new gas issue that has occurred since the gas pressure has been bought back up. Need help need heat upstairs.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Nov 19, 2008, 12:20 PM
    Brand and Exact model of thermostat? Cannot do much without that.

    The problem you are having is with the thermostat not the gas at this time.

    You have dual thermostats?

    Do you have one or two furnaces?

    Are these furnaces or a boiler system?

    Put the parts from the thermostats back where ever you changed them from.

    Post back with the info.
    jwigfall's Avatar
    jwigfall Posts: 7, Reputation: 1
    New Member
     
    #3

    Nov 19, 2008, 12:36 PM

    The Thermostats are Honeywell Chromotherm III's. There are two separate thermostats, two separate furnaces. Parts have already been return to rightful units.
    jwigfall's Avatar
    jwigfall Posts: 7, Reputation: 1
    New Member
     
    #4

    Nov 19, 2008, 12:58 PM
    Quote Originally Posted by hvac1000 View Post
    Brand and Exact model of thermostat? Cannot do much without that.

    The problem you are having is with the thermostat not the gas at this time.

    You have dual thermostats?

    Do you have one or two furnaces?

    Are these furnaces or a boiler system?

    Put the parts from the thermostats back where ever you changed them from.

    Post back with the info.
    The Brand is a Honeywell Chromoterm III. There are two separate thermostats and two separate furnaces in the home. The parts have been return to their rightful units.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Nov 19, 2008, 01:42 PM
    Honeywell Chromotherm III's does not help

    I have to look up by exact model number.

    Honeywell has made 20 different series 3 thermostats. I will also need the subbase model number. That is the item the thermostat hooks to on the wall.
    jwigfall's Avatar
    jwigfall Posts: 7, Reputation: 1
    New Member
     
    #6

    Nov 19, 2008, 05:26 PM
    The Honeywell Thermostat model number is T8601C1047. Not sure but there maybe a 1 after the seven but it is turned horizontal.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #7

    Nov 19, 2008, 06:07 PM
    Quote Originally Posted by jwigfall View Post
    The Honeywell Thermostat model number is T8601C1047. Not sure but there maybe a 1 after the seven but it is turned horizontal.

    Your systems AC power has been lost

    Read page 3

    http://customer.honeywell.com/techli...0s/69-0577.pdf
    jwigfall's Avatar
    jwigfall Posts: 7, Reputation: 1
    New Member
     
    #8

    Nov 19, 2008, 06:38 PM
    Quote Originally Posted by hvac1000 View Post
    Your systems AC power has been lost

    Read page 3

    http://customer.honeywell.com/techli...0s/69-0577.pdf
    Is there anything I can do to reset the AC power besides the circuit breakers. Or is there something on the heater that can be reset. It was just working yesterday morning, it seems like there something I can do.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #9

    Nov 19, 2008, 07:01 PM
    OK first install new fresh batterys correctly into the thermostat. Then post back with the results.
    jwigfall's Avatar
    jwigfall Posts: 7, Reputation: 1
    New Member
     
    #10

    Nov 19, 2008, 07:29 PM
    Quote Originally Posted by hvac1000 View Post
    OK first install new fresh batterys correctly into the thermostat. Then post back with the results.
    New batteries installed. Thermostat switches on & off showing Temp then -AC.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #11

    Nov 19, 2008, 07:42 PM
    Looks like you have lost the A/C power at the furnace. It could be a transformer or the furnace power switch is turned to the off position. It could also be a broken wire going to the thermostat.
    jwigfall's Avatar
    jwigfall Posts: 7, Reputation: 1
    New Member
     
    #12

    Nov 20, 2008, 09:42 AM
    Quote Originally Posted by jwigfall View Post
    New batteries installed. Thermostat switches on & off showing Temp then -AC.
    New batteries are installed and I performed the self test of page 3 & 4 of the Honeywell spec sheet. It tries to start but I still get the -AC on the screen. I also measured the AC test points of C & R and it measured 28.5 Vac. There are contact points that transfer power and info from the thermostat to the base but I don't which pins are for what and the Honeywell spec sheet never covered that. Are there any other measurements I can make?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #13

    Nov 20, 2008, 09:55 AM

    Guessing: Could it be an Air Cleaner warning message?

    In other words time to reset and change the air cleaner. This should only be a warning though.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #14

    Nov 20, 2008, 10:24 AM
    If you have followed the info I have posted from the Honeywell site I do not know what else to tell you. It might be thermostat time.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

No display is showing on my thermostat [ 2 Answers ]

I have a honeywell thermostat and my display is not working. Is my thermostat bad?

Bryant furnace: thermostat showing "AC", house cold, fixed (for now.) [ 1 Answers ]

System: Bryant 333BAV 80 plus furnace, 10 yrs old, with Honeywell Chromotherm III thermostat. No problems with either in the past. Minnesota. January. Upon waking up this morning, found the house was 58 degrees, with set point at 68. Checking the thermostat, found it was showing "AC" (power...

When you start showing in pregnancy? [ 1 Answers ]

I think I might be pregnant. I was wondering what's the earliest you start showing or feeling bigger?

Hdd not showing in disk management but showing in device manager [ 1 Answers ]

I have my friend's hdd which crashed few daz ago then I connected it to my PC as slave but now its in the device manager and bios though not showing in MY COMPUTER,DISK MANAGEMENT.. help

My honeywell thermostat is showing a code of -AC [ 1 Answers ]

My honeywell thermostat is showing a code of -AC what does that mean?


View more questions Search