    Buca75's Avatar
    Buca75 Posts: 3, Reputation: 1
    New Member
     
    #1

    Nov 18, 2008, 05:57 PM
    Blower fan does not always come on
    Hello,

    The blower on my furnace doesn't always start. After the burners run for several seconds, I hear a click noise (from the relay?) every time but then the blower doesn't always start up and eventually the whole thing turns off for a few minutes. Sometimes it works perfectly fine. Also, the blower starts every time I turn it on manually (so at least I'm able to heat my house).

    I'm thinking of replacing the fan control module but it's not cheap so any tips or suggestions would be greatly appreciated.

    Some info:
    Kenmore natural gas furnace (approximately 10 years old).
    Heatcraft fan control module.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Nov 18, 2008, 06:29 PM
    The control you mentioned does control the fan with a built in relay and if you hear the click of that relay and the fan does not run that is the problem. Since the blower motor operates on manual it seems that the motor itself is not the problem.
    letmetellu's Avatar
    letmetellu Posts: 3,151, Reputation: 317
    Ultra Member
     
    #3

    Nov 18, 2008, 07:21 PM

    If this is a capacitor start motor it could be a bad capacitor. The capacitor is very cheap and would be worth buying one just to see if that is the problem. Make sure you buy one that is the same as what is there now.
    Buca75's Avatar
    Buca75 Posts: 3, Reputation: 1
    New Member
     
    #4

    Nov 18, 2008, 08:13 PM

    Thank you for the replies.

    If it were just the capacitor, I'm guessing I would have problems starting the blower manually (which is currently how I'm heating the place). Correct me if I'm wrong here.

    If it is the fan control module, is there any likely hood of repairing it? Would removing it and cleaning it do anything?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Nov 18, 2008, 08:19 PM
    It is not the capacitor in your case but a defective capacitor can cause motor problems.

    The fan control modual contains many parts that are usually not available at a local Radio Shack so usually you are out of luck when it comes to a repair. Replacement is usually the only possibility.
    Buca75's Avatar
    Buca75 Posts: 3, Reputation: 1
    New Member
     
    #6

    Nov 18, 2008, 08:19 PM
    Some more info...

    Furnace
    Name: Kenmore
    Model: CUG5075BFA2

    Fan control module
    Name: Heatcraft
    Model: FTC5-EH01
    JohnButch's Avatar
    JohnButch Posts: 1, Reputation: 1
    New Member
     
    #7

    Mar 4, 2010, 06:13 PM
    My sons furnace failed today, the fan motor wouldn't run in auto but would run manual, I pulled the fan relay out (ftc5-eh01) & removed the back , I found (4) bad solder joints on the PC board. I soldered all (4) joints & that took care of the problem.
    Brigittesbm's Avatar
    Brigittesbm Posts: 1, Reputation: 1
    New Member
     
    #8

    Sep 2, 2010, 12:29 PM
    Does anyone know where I can buy this part??
    GasMan2000's Avatar
    GasMan2000 Posts: 1, Reputation: 1
    New Member
     
    #9

    Sep 5, 2012, 05:34 PM
    Also looking for a replacement for this poorly made part: HeatCraft model FTC5-EHO1 or HeatCraft model FTC5-EH01.

    Does anyone have a source?
    crokante's Avatar
    crokante Posts: 3, Reputation: 1
    New Member
     
    #10

    Apr 16, 2013, 12:39 PM
    I have a similar problem.

    The furnace start fine but not the fan. After 3 minutes heating the unit turn off itself and the fan start working for 30 second and the goes off.

    A workaround (mikey mouse) I found is doing a bridge between the 1st contact and the 5th one (starting from the right) -see pic:

    https://www.dropbox.com/s/8q3wss0l5uvjls8/Fan%20Module-3.JPG?n=10386083

    This way the unit works fine the whole day.

    But... if I want to use the Air Conditiones cooler, I need to restore the connection to its original configuration.

    Any recommendation about replacing the fan module HeatCraft model FTC5-EHO1 or/and the capacitor (see pic: https://www.dropbox.com/s/ocr5ondkigq4yap/Capacitor-1.JPG?m )

    Also, I can find any place to buy those replacement parts (ebay, Google, etc.)

    Thanks so much for any advice!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Blower fan [ 11 Answers ]

I have a lennox g2003e75 that has just started giving me trouble. The blower fan will not engage. It does not engage in either the heat, cool, or on positions. The outside unit comes on, and the copper tube gets cold. The blower clicks, starts to turn, and immediately shuts off. There is...

Blower not working and blower running all the time [ 2 Answers ]

I have a Lennox electric furnace that's about 10 years old or so, the elements come on but no blower. There is a summer fan switch that will make the blower run when switched on, but it will not come on with a call for heat. Also at my work, there is a york gas pack that is probably 15 years old....

AC blower fan [ 4 Answers ]

When my AC turns on the fan doesn't always turn on when it is set to auto. Sometimes it does sometimes it doesn't. I can set it to on and the same thing happens. If it turns on It will stay on and turn back off with the rest of the unit. Right now I have to run the fan all the time so the unit...

Blower [ 1 Answers ]

I'm talking about the main blower,my system is only 12 yrs old

Blower [ 3 Answers ]

When the blower starts up it seems to have a hard time getting started. (makes a noise like: wa... wa... wa.. wa) and then runs normally. Doesn't do this every time but maybe one out of four starts. Is motor going or some other reason? Thanks


View more questions Search