    Recessed light awg
    Hi,

    I bought a case of recessed lights that says' max (4) 12 awg through branch circuit conductors. The light circuit that I was planning of connecting to is 14 awg and connect to 20amps breaker. Entire house was wired with 14 awg (lights and plugs) with 20 amps breaker. Is there anyway I can used these lights using 14 awg? Also what does AC only means.

    Thanks
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #2

    Nov 12, 2008, 10:37 PM
    Quote Originally Posted by adrien02 View Post
    Hi,

    I bought a case of recessed lights that says' max (4) 12 awg through branch circuit conductors. The light circuit that I was planning of connecting to is 14 awg and connect to 20amps breaker. Entire house was wired with 14 awg (lights and plugs) with 20 amps breaker. Is there anyway I can used these lights using 14 awg? Also what does AC only means.

    Thanks
    -The 4 (12) conductors is a set number of conductors allowed in the fixture box per manufacture specifications, and depending on the box per NEC.
    -#14AWG cannot be served by a 20A breaker per section 240.4. >Use a single pole 15A breaker only, or up size your conductor to #12 if you want to use a 20A breaker<
    -Yes you can use the 14AWG for the lighting, unless you have a local code saying otherwise
    -AC=Alternating Current or a-c current: It's a current that does not always flow in the same direction. To be practical, I can say all electricity used today is AC, because it's cheaper to produce, and more usable (or versatile).
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Nov 13, 2008, 06:15 AM
    I really need to reinforce what Washington has said about the #14 wire on 20 amp breakers.

    If this is true, you have a serious issue that needs to be corrected.

    20 amp breakers on #14 wire can cause overload of the #14 wire, as it should not be on any breaker larger than a 15 amp.

    Any #14 wire with a 20 amp breaker needs to be changed to a 15 amp breaker.

    How old is this house?

    Who did the wiring?

    Who ever did this needs to loose their license.
    adrien02's Avatar
    adrien02 Posts: 6, Reputation: 1
    New Member
     
    #4

    Nov 13, 2008, 10:42 AM
    Sorry guys, I misstated my question.

    It should have stated "max (4) 14 awg through branch circuit conductors" and planning of connecting to is 12 awg with 20amps breaker. Can I connect the light using 12 awg or 14 awg.

    You stated that it was okay to go from a 14awg to 12awg on the same circuit (15 amps). (if permit allows).
    Is it because if the circuit draws more the 15amp the breaker will trip (both wire can handle 15amps).

    On the other hand , is it not okay to go from a 12 awg to 14awg on the same circuit (20 amp)? What if the circuit draws more the 15amps but less than 20amps, the 14awg can not handle this current and will it start to disintegrate (possible starting a fire) since the breaker will never trip.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #5

    Nov 13, 2008, 02:57 PM

    Adrien,

    Stop and re-read the postings please.

    No one said it was okay to mix #14 and #12 gauge conductors as a blanket statement.

    You can mix #14 and #12 gauge providing that you use a 15 amp breaker and nothing larger.

    If you want to use a 20 amp breaker, the #14 gauge conductors in that particular circuit must be replaced by #12 gauge conductors.

    If you run 20 amps through #14 gauge conductors, you will be creating a serious fire hazard. #14 AWG conductors will get to hot with 20 amps running through them.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Recessed Lights: Light Switch does not work. [ 12 Answers ]

Hello, I just installed 2 IC recessed lighting in our kitchen. One of the hole where I attached one of the recessed lights had 2 metallic flexible cables. 1 of which had 1 white, 1 red, 1 orange, and 1 green. The other cable had 1 white, 1 red, and 1 green. The recessed fixture has 3 wires: White,...

Recessed Light and Air Duct [ 2 Answers ]

I recently started a project to install recessed light in my family room. Everything was checked and planned. All holes were cut and align properly... until the last hole. It appear that I have an air duct running right on top it. It's big and it has black plastic wrap enclosure. One of...

Recessed light installation [ 1 Answers ]

I posted a message here several weeks ago about a contractor who simply stapled the Bx cable for recessed lights to the bottom of the joist rather than running it through the joist (1st floor of 2 story home). The electrician has finally agreed to come back after much prodding and redo the work...

Recessed light in shower, GFI? [ 5 Answers ]

Hi there. I I want to put a recessed light above my shower, does it need to be gfi protected? If so, what is the easiest way to do this, since it can't be on the bathrooms regular light circuit. I was thinking switchleg out of the bathroom gfi receptacle? Also, my panel is on the opposite...

Recessed light suddenly stop working... [ 5 Answers ]

Hi. My daughter's room has 6 recessed lights that are controlled by a dimmer switch. Today, I went to turn them on (they have worked fine up until today), we recently had new doors installed and I was spackling, and when I tried to turn the lights on, the dimmer switch wouldn't turn the light's on...


View more questions Search