Air Vent Configuration
When we removed a kitchen cupboard to take out a stovetop and replace it with a free standing range, we found this pipe on the floor. Apparently it is an air vent for the kitchen sink. Question:
Can this pipe be re-routed under the floor at the edge of one cupboard and come back up to be re-joined at the edge of the other cupboard so as to allow the new oven to fit to the wall? See attachment.
|
|
 |
Home Repair & Remodeling Expert
|
|
Nov 9, 2008, 03:33 PM
|
|
Yes you can reroute the pipe but you must confirm that it is a dry vent to begin with. You can't reroute downward if this is a wet vent, it would create a Traplike pocket of water and no longer vent.
|
|
 |
Eternal Plumber
|
|
Nov 9, 2008, 03:57 PM
|
|
Something's not right here Bob. The kitchen vent's on the floor? If that's the laterial drain from the sink it should be 18" off the floor and if it's a vent it should be vertical.
I wanna see a picture of the sink cabinet and drainage hook up!! Cheers, Tom
|
|
 |
Home Repair & Remodeling Expert
|
|
Nov 9, 2008, 07:04 PM
|
|
Could be a horizontal leg of a vent that goes vertical elsewhere. AMK needs to do more homework before cutting the unknown pipe.
|
|
 |
Eternal Plumber
|
|
Nov 10, 2008, 05:13 AM
|
|
 Originally Posted by ballengerb1
Could be a horizontal leg of a vent that goes vertical elsewhere. AMK needs to do more homework before cutting the unknown pipe.
If that's a kitchen "horizontal leg of a vent that goes vertical elsewhere" Then I'm looking at a "S" trap Unless it's a vent from a basement fixture. I wanna see a picture of the kitchen sink drainage!! Cheers, Tom
|
|
 |
New Member
|
|
Nov 10, 2008, 07:59 AM
|
|
Thanks for your answers!
According to the builder, the vent is attached at a 90 degree angle from the drain, under the cabinets, on the floor. It goes around behind the cupboards and then into a vertical stack.
I am attching pictures of the drain but I don't think they help much.
|
|
 |
Eternal Plumber
|
|
Nov 10, 2008, 09:01 AM
|
|
AMK,
Thank you for the pictures. It's all clear now. You may not route it under the floor and then come back up. That would put a running trap in the vent and that's a big no-no. You will have to lower the trap and run the vent under the floor unless you could install a offset that could run through the dishwasher under the tub. Good luck tom
|
|
 |
New Member
|
|
Nov 10, 2008, 09:11 AM
|
|
If it is just air, could the pipe be 90 degrees into the wall and then back out so that it is still on the same plane?
|
|
 |
Home Repair & Remodeling Expert
|
|
Nov 10, 2008, 06:59 PM
|
|
I don't see any trap in your pics, where is the trap?
Bob! The trap's located under the floor line. That's why he could run the vent on top of the floor.
|
|
 |
New Member
|
|
Nov 11, 2008, 06:53 AM
|
|
OK you guys are confusing me.
If it is an air vent can it or can it not be diverted either into the wall or under the floor and back up again?
Thanks.
|
|
 |
Eternal Plumber
|
|
Nov 11, 2008, 07:07 AM
|
|
 Originally Posted by AMK1834
OK you guys are confusing me.
If it is an air vent can it or can it not be diverted either into the wall or under the floor and back up again?
Thanks.
You may not route it under the floor and then come back up. That would put a running trap in the vent and that's a big no-no. You will have to lower the trap and run the vent under the floor unless you could install a offset that could run through the dishwasher under the tub.
AMK1834 If it is just air, could the pipe be 90 degrees into the wall and then back out so that it is still on the same plane?
Now THAT you could do providing you maintained slope. You just can't drop under the floor and back up again. There's where you make a mistake in judgement. It's not just air. Why do you think we give vents pitch back to the drain? Becase rain water can drain back to be disposed up. If you built a running trap by dropping down under the floor and then come back up the rain water would be trapped and build up to block the vent. Congratulations! You have come up with your own solution. Elbo into the wall and back out again. Just maintain some pitch on the offset and you'll be just fine. I hope I;ve explained everything to your satisfaction.
Good luck and thank you for rating my reply. Tom
|
|
 |
New Member
|
|
Nov 11, 2008, 09:14 AM
|
|
Thanks for everything!
|
|
 |
Home Repair & Remodeling Expert
|
|
Nov 11, 2008, 05:12 PM
|
|
Vents can be wet vents or dry vents. A dry vent never , ever has awter in it and they can not go down and back up. A dry vent can go under the floor but like Tom points out, your trap is under the floor and we can't see it or how its is connected. Can you get pics from below the floor? I need to totally defer to Tom since I have never seen a setup like this. Tom's the plumber here
|
|
 |
Plumbing Expert
|
|
Nov 11, 2008, 05:28 PM
|
|
I'm a bit confused here too. I see no trap under the sink(above the floor) Is it possible that your original pic is of the drain. Possibly. You can offset it into the wall if you desire. But I see a lack of trap and vent if I am right about your original picture. Looks like they just ran the drain in the toespace of the cabinets. Need more pics and info as to what you really have here.
|
|
 |
Ultra Member
|
|
Nov 11, 2008, 05:38 PM
|
|
In my opinion you could cut the pipe and put it in the wall on the same level that it is on now. If at all possible I would use two 45 degree ells on each end of the cut to turn it back into the wall.
I am a little confused about where the trap or traps are for the sink. Also I would like to know what the wye is for in the pictures that show under the sink, it may be the drain from the dishwasher, it is hard to tell
|
|
 |
Ultra Member
|
|
Nov 11, 2008, 05:42 PM
|
|
After looking at the picture showing where the range is going I studied the ABS pipe and to me it looks that the slope on that pipe is from left to right, so do you have something that has a drain line in the area left of the range, something like the condensate from the air condiitioner, of maybe a water softner?
|
|
 |
Plumbing Expert
|
|
Nov 11, 2008, 05:48 PM
|
|
Looks like the wye is for dishwasher, and a tee for a cleanout right at base of cabinet. No trap no vent.( not even an aav, which doesn't matter because there is no trap). I do agree with letmetellu. If your current sink works just fine, then you will have no problem running line into wall for a distance and back out, as long as you keep same slope as you have now on whatever that pipe is. You will have to drill some holes in the studs in the wall, or notch the studs(would prefer drilling holes).
|
|
 |
Senior Plumbing Expert
|
|
Nov 12, 2008, 05:24 AM
|
|
Hi all...
My biggest concern here isn't the drain/vent as much as it is an UNCAPPED GAS LINE..? AMK1834.. please install the flare fitting back into the gas line and then CAP the end of the gas pipe. Some shutoffs fail and sometimes when working around the pipe shutoff handle can get snagged... just as an extra precaution as you deal with the vent, plug that gas line... ;)
Good luck...
MARK
|
|
 |
Plumbing Expert
|
|
Nov 12, 2008, 07:40 AM
|
|
It is kitchen drain that runs under kick plates. No, you cannot reroute it under the floor unless you reroute entire run under the cabinets. You will be better off if you 45 it in/out of the wall to by-pass stove opening. If you are lucky, you have trap under the kick plate. But considering overall look of the work done, it may not be so...
Btw: Who was the original plumber ? Mickey Mouse ?
|
|
 |
Senior Plumbing Expert
|
|
Nov 12, 2008, 08:11 AM
|
|
I think Milo called this one... :)
Hopefully AMK1834 will return
Nice job!
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Attic vent and vent pipe leaks through roof
[ 7 Answers ]
Hello:
I have water leaking down through the attic vents and white PVC vent pipes. What is the best way to repair these leaks? Can repairs be made from inside the attic? Should the vents be replaced (they are plastic)?
Thank you!:(
Laundry Pump vent hookup. How? - no vent access
[ 9 Answers ]
I have a Laundry Tray Pump System connected to my wash tub in my fifteen year old townhome's basement. I was recently informed that it was not properly installed because I never connected the vent pipe from the pump.
I had some one look at it and was told that the house's vent system (which...
Drain vent configuration for a basement shower
[ 1 Answers ]
I have a basement shower that does not drain quickly enough, and I am guessing it is due to my vent configuration.
The shower uses 2" plastic piping with trap, which then connects to 1 1/2" copper piping. That pipe connects to another copper pipe which is connected to the kitchen and laundry on...
Vent pipe configuration
[ 17 Answers ]
We are remodeling our kitchen and need to move or sink about 8 feet from the original spot. I'd like to use the existing vent through the roof so that I don't have to make another whole in the roof. I've attached a picture of the setup I'm planning. Will this work since I'm in NJ?
Vent diagram - does this meet code (see pic)? Vent runs below actual drain
[ 4 Answers ]
The schematic below should make it clear the configuration I would like to use. Basically, I would like to keep the vent under the floor for a little ways, so it pops up in a better location. I cannot easily move the 2" drain location going down and would rather not go straight up from the...
View more questions
Search
|