    Heater tripping the breaker
    I recently got some info in here from some knowledged fellas about a 240 electrical heater I was hooking up and had great success in getting it hooked up and running. It has ran fine until about 3 days ago it started to throw the breaker. Its rated at 42.2 amps and was told with electrical heaters to rate them 125% which brought it to 52.75 amps. I wired it straight into the panel with 6 awg wire and am using a 60 amp breaker. Any ideas on why it would start tripping the breaker?. And do you think it was solve the problem if I stepped up to a 70 amp breaker or would this cause more problems or even worse be hazardous of fire?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Nov 7, 2008, 03:33 AM
    Could be a defective breaker,or, more likely there is a loose connection at the breaker.

    Do not just arbitrarily change the breaker to a 70 amp, that will require the wire to be replaced also.

    Always a chance there is a short circuit in the feeder or heater.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #3

    Nov 7, 2008, 07:38 PM
    If you can borrow a clamp on ammeter, you can determine what the load is while the heater is running. If you can determine what the actual heater load is, you can determine whether it's a heater issue or a breaker issue. Check for loose connections at the breaker, and signs of overheating with the wiring. (burnt insulation, darkening of the insulation) Double check your heater nameplate for the correct voltage and amperage. Do you have an owners manual with the specs? Was the breaker used for something else at one time? Does the breaker get hot to the touch when the heater is running? Let us know what you find out.
    kich1031's Avatar
    kich1031 Posts: 26, Reputation: 3
    New Member
     
    #4

    Nov 8, 2008, 03:51 AM

    You never want to upgrade the breaker... the breaker may be rated for 70 amps but the wire is only rated got 60 amps which means the wire will fail (catch fire, melt) before the breaker trips.
    wildandblue's Avatar
    wildandblue Posts: 663, Reputation: 57
    Senior Member
     
    #5

    Nov 8, 2008, 09:21 AM

    Be sure you have a new unit, not a factory reconditioned one that someone else returned because they had problems with it too. A 240 circuit is basically 2 120's side by side so I suspect there could be a short in your unit or in your wire where the two 120's are touching each other, or maybe a damp location where moisture is causing trouble? Sometimes the wire can get twisted being unwound from the coil, like an extension cord can get ruined by too much winding and unwinding.
    caibuadday's Avatar
    caibuadday Posts: 460, Reputation: 10
    Full Member
     
    #6

    Nov 8, 2008, 02:26 PM
    Also when the heater doesnot disipate its own heat fast enough the breaker may trip
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #7

    Nov 9, 2008, 07:15 AM
    To clarify this statement:

    Quote Originally Posted by caibuadday View Post
    also when the heater doesnot disipate its own heat fast enough the breaker may trip

    A heating element that does not dissipate all of it's heat will not cause the load to increase at all, and cause a breaker to trip.

    In this event of a heater not dissipating heat is caused by two typical problems, either the air flow is blocked by an obstruction, or the fan motor is not operating and forcing air over the elements. Either event will cause the heat to activate the High Temperature Limit switch, built into each electric heater, and shut down the power to the elements.

    The breaker will not trip unless there is a short circuit or an overload.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Breaker keeps tripping [ 24 Answers ]

I need to figure this out. I have two 15 amp space heaters in my garage and when I turn them both on it throws the breaker. The breaker at box for this is rated at 20amps. I have been told that I can run both on high and won't throw the breaker. I also replaced the old breaker with a new one (same...

Breaker keeps tripping when I run heater [ 1 Answers ]

My 6o amp breaker keeps tripping after about 15 minutes of running my electric heater. It is the kind that is in a closet in a mobile home. It ran fine last winter and suddenly started tripping breaker. The heater is fairly new, about 4 years old. I am trying to pin point the problem so I can...

Breaker keeps tripping [ 1 Answers ]

I have a 40 amp double pole breaker in my main service panel which feeds a pony box in my attic. A window air conditioner is tripping the 40 amp breaker in the main panel before the 10 amp breaker in the pony box. The 10 amp breaker services two receptacles and one track light. The track light has...

Breaker not tripping [ 3 Answers ]

Hello, I was trying to install a light fixture and when I was done connecting the wires, I lifted the fixture towards the ceiling to mount it and there was a spark and caused a black mark on the ceiling. Would that cause the breaker to trip? And should I be concerned about the wiring causing a...

Breaker keeps tripping [ 1 Answers ]

We have recently purchesed a Vits spa from some one. When we did we replaced the heat element . It has worked well for the last 6 weeks but now it it tripping the breaker on the heater. Any suggestions.


View more questions Search