    I just moved in a house, and pretty new to all applicances inside.

    I changed the old mercury thermostat to a programmable Honeywell one, because the old one can't stop furnace unless lasting a long time, say half an hour. One night the furnace continued burning until room temperature reached very hot degree even can't sleep.

    The new Honeywell programmable thermostat seems good, usually works normally, but sometimes it seemed can't stop furnace neither. The room temperature will surpass 2-4 degree than the set one. For example, the set temperature 22 degree, the heated room tem. 25 degree. If I turn off heat at thermostat, it will always stop furnace after around half an hour. Is it normal?

    I am really messy about these. Hope for help.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Oct 29, 2008, 10:10 AM
    The thermostat is wired and set correctly should turn the furnace off and on at the prescribed settings. In some cases there are electronic adjustments you can make in the programing of the thermostat. Read your directions to find out.

    If this is doing the same thing with the new thermostat that the old thermostat was doing it could be some other problem with the furnace.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring a furnace thermostat to manually operate the furnace fan [ 2 Answers ]

I have two wires connected to my furnace thermostat. There is a place labeled G on the thermostat. Can I simply run a wire from the G terminal on my thermostat to the terminal labeled G on my furnace fan relay to operate the fan separately?

No heat from vents Heil , after putting in new thermostat furnace will not turn on [ 14 Answers ]

New 100,000 80% Heil furnace put in 12-19-1997 - no heat coming out of the vents. Diagnosis from 2 different people was : 1. trace the wiring from the thermostat and the blower, because the blower works, but there is no heat so somehow the thermostat is not sending the message to the...

Honeywell thermostat works and trane heatpump and furnace won't turn on [ 1 Answers ]

When I turn on my honeywell thermostat it says its on, but the furnace and the heatpump don't don't turn on. What could the problem be?

Thermostat turns on furnace and then thermostat shuts back to HOLD [ 7 Answers ]

I believe that when we re-run the program with the correct date and time, if the temp has to go up, the furnace runs until it gets the appropriate temp, then it turns off and when it does that, the thermostat also turns off going to the HOLD state.:confused:

Changed Thermostat will not automatically turn Furnace on [ 1 Answers ]

We changed our old honeywell thermostat (with mercury) to an updated honeywell thermostat (with no mercury) CT87K. After we changed the thermostat the furnace will not automatically kick on and it actually shut off so we had to hit the reset button. The furnace at times now will turn of if we put...


View more questions Search