    Old electric furnace partially heating
    Greetings,

    I have an old electric furnace located in my attic. I cannot determine the mfg/model, but estimate the unit to be ~20+ years old. We have owned the house for 2 1/2 years and have had heater problems each season. In the last two years we have replaced burned out heating elements and the heating sequencers. This year we called a service company and they diagnosed a burnt out element and a bad sequencer. The element was replaced, but I decided to do my own diagnostics on the sequencer before paying (again) for another one. I'm not an HVAC guy but very handy with a voltage meter and home improvement/repairs. Here's what I've found and it doesn't seem correct to me. Can someone provide an opinion on the findings.

    Electric furnace info:
    Location - Attic
    Mfg / model - Unknown
    Age - Estimated 20 - 25+ years
    Heating type - Electric
    Heating element wattage - 5Kw
    Number of elements - 3
    Sequencer - "Quad"
    Number of sequencers - 1

    Sequencer diagnostics and wiring info:
    Sequencer - two 2-stack units mounted on a base plate. On the base plate is this information:
    15SH22 309576
    H1-110 C1-110

    Sequencer #1 information (from top of sequencer):
    T-O-D
    12SH22 H24v
    308771 A0546

    Sequencer #2 information (from top of sequencer):
    T-O-D
    12SH22 H24v
    308734 A0548

    Sequencer 1 = M1 & M2, M3 & M4, 24V + / -
    Sequencer 2 = M5 & M6, M7 & M8, 24V + / - (the 24v terminals are jumped across pos -> pos, negative -> negative between sequencers)


    Diagnostics results with the unit cycling on / off:
    With the unit powered off (not calling for heat) M1 / M2 and M3 / M4 carry 240v. When the unit powers on these go to 0v and do not carry voltage until the unit cycles off again.
    With the unit powered on (calling for heat) M5 / M6 carry 0v and ~90s later carry 240v. M7 / M8 carry 120v then go to 0v ~90s later, then a little longer go back to 120v.

    Question: Is it normal to have sequencers "normally closed" as with M1 / M2 & M3 / M4? Also, is it normal to have a mix of 240v & 120v running across a sequencer stack?


    Here's the wiring. The colors are as best as I can determine. Most wires are faded and hard to distinguish the original color:
    Note: High temp thermos & heating elements are designated 1 - 3 for information only. I'm presuming they are wired correctly.

    There are two (double) breakers at the unit. Breaker 1 = 40amp, breaker 2 = 30amp.
    Breaker 1 - Hot (black) -> M1
    Breaker 1 - Hot (black) -> M5
    Breaker 1 - Hot (black) -> Wiring harness
    Breaker 1 - Common (white) -> Wiring harness
    Breaker 1 - Common (orange) -> High temp thermo #1
    Breaker 1 - Common (orange) -> High temp thermo #2

    Breaker 2 - Hot (black) -> M7
    Breaker 2 - Common (orange) -> High temp thermo #3

    M2 -> (purple) Heating element #1
    M3 -> (blue, maybe violet) Wiring harness
    M4 -> (brown, maybe violet) Wiring harness
    M6 -> (purple) Heating element #2
    M8 -> (purple) Heating element #3

    High temp thermo #1 -> (red) Heating element #1
    High temp thermo #2 -> (red) Heating element #2
    High temp thermo #3 -> (red) Wiring Harness

    Sequencer 1 - (yellow) 24v+ -> Wiring harness (to fan/thermostat relay box)
    Sequencer 2 - (violet, maybe gray) 24v+ -> Wiring harness (to fan/thermostat relay box)
    Sequencer 1 - (purple) 24v- -> Wiring harness (to fan/thermostat relay box)
    Sequencer 2 - (purple) 24v- -> Pigtail from 24v-

    Question: Is it possible that the 24v wires are simply reversed, in turn causing the normally closed condition on sequencer #1?

    Thanks in advance for any comments and feedback.

    Sincerely,
    Greg Dotts
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Oct 27, 2008, 12:11 PM
    See other post

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Old electric furnace partially heating [ 7 Answers ]

Greetings, I have an old electric furnace located in my attic. I cannot determine the mfg/model, but estimate the unit to be ~20+ years old. We have owned the house for 2 1/2 years and have had heater problems each season. In the last two years we have replaced burned out heating elements and...

Day & Night electric furnace not heating well [ 1 Answers ]

My Day & Night 517E electric furnace runs a long time and does not heat as well as it used to. This is relatively recent. The air from the registers _seems_ cooler and the furnace does not reach it set point most of the time. During the day, it will sometimes get to the set point, but at night,...

Cost of converting electric heating to gas heating [ 2 Answers ]

I am buying a house with electric heat. I have heard it can be a lot more expensive than gas. What would be the cost of converting the house to gas heating and a/c?

Electric Furnace - heating element [ 3 Answers ]

I am trying to convert from my broken boiler furnace to an electric furnace. I have central air and all the vents from that. Can I just buy a heating element and put it into the air handler? If I can, how do I know what size heating element to buy? The search on the internet gave 10 and 15 KW...

Electric heating to gas heating conversion [ 1 Answers ]

Hi All, I am new to the site and wanted to know if anyone could assist me with a general quote for electric heating to gas heating conversion on one floor of a three story apartment building. Here are the specifics: 1000 square foot area; 8 rooms; 6 electric baseboards. Thanks.


View more questions Search