    Why does my central air blower fan runs continuously?
    I have Heil central air system. My blower motor (fan) is been running continuously, either in AC/HEAT OR ON/AUTO MODE. Only way to shut the fan is by switching the emergency switch to off.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #2

    Oct 25, 2008, 05:04 PM

    Does the burner come on when in call for heat?
    Kash78's Avatar
    Kash78 Posts: 5, Reputation: 1
    New Member
     
    #3

    Oct 26, 2008, 09:07 PM

    Yes, the burner does come on when called for heat...
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Oct 26, 2008, 09:19 PM
    It could be the fan and limit control or the A/C blower relay.
    Kash78's Avatar
    Kash78 Posts: 5, Reputation: 1
    New Member
     
    #5

    Oct 27, 2008, 02:47 PM
    I looked around the blower motor and I don't see any relay. On the blower motor there is a square box with wires going to it and on top of this box there is a silver oval shape component, don't know if that's a relay or a capacitor. When I place the switch to on and auto on my thermostate, I hear a clicking sound from this oval shape component... any ideas what this thing is for? There is also engraving on it: 240v and some letters and numbers like uf5 and so on... My unit was installed in 1984, made by HEIL...
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Oct 27, 2008, 03:36 PM
    The silver oval thing is the capacitor.

    Look in that box and see if there is a relay in there. It is possible the contacts are stuck/burnt together. Turn the power off before you go playing in the box!
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #7

    Oct 27, 2008, 06:05 PM

    Do you see a squar or rectangular shaped flat piece mounted on the inside of the top part of the furnace directly above the burners. There would be two wires connected to it.
    Kash78's Avatar
    Kash78 Posts: 5, Reputation: 1
    New Member
     
    #8

    Oct 29, 2008, 01:13 PM
    I looked around the main junction box next to the red toggle sw and I saw the limit control box square shape with honeywell label on it... it has four wires going to it from the main junction box colored yellow-brown and black-black... while the fan blower motor was running in auto mode continuously, I tapped the limit control box and the fan stopped running right away... I'm thinking the limit control should be my fix... I also saw the wire diagram next to the main junction box and I did not see any relay on this diagram, just a capacitor on the blower motor and a transformer on the main junction and also thermostate for gas valve mounted next to the transformer and then the fan/limit control box... I will replace the limit control and see what heppens... thanks for helping me troubleshoot this problem...
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #9

    Oct 29, 2008, 02:38 PM
    I believe you are headed in the correct direction.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #10

    Oct 29, 2008, 02:43 PM

    You have found your problem, glad we could help.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

AC Inside Blower Stops, Condenser runs continuously Until Entire Unit shut off & Reset [ 6 Answers ]

I have a Trane compressor outside. The unit comes on and the interior blower comes on for a few hours and then stops blowing. I tried to turn on the fan via the thrmostat and it does not work when it shuts down but otherwise works fine so its not a wiring problem. The outside unit continues to...

Coleman hvac blower runs continuously. [ 3 Answers ]

We have a 1998 mobile home with a coleman hvac. For the past 6 months the blower has not turned off even though the air itself has? Does anyone have any suggestions to what might be causing this?

Central AC not blowing inside, outside fan runs continuously. [ 2 Answers ]

My ac guy has added freon, cleaned the outside coil, replaced the inside fan motor, and replaced thermostat. The outside fan will kick on, but the inside fan doesn't kick on. If I shut the unit OFF, then back ON at the thermostat sometimes it will kick the inside air on and it will be fine. But,...

Central air conditioner runs for over 1 hour before kicking off is this normal? [ 1 Answers ]

My central air conditioner Heat pump just started running for over an hour before kicking off and only cools 1 degree.. we had thermostat replaced 2 days before this started happening... what should we do?

Central A/C outside runs but compressor kicks on and off [ 2 Answers ]

Just cleaned the complete system, at furnace and outside. Had unit serviced (Sears Kenmore) for low freon, now when I turn on A/C the fan outside runs OK but the compressor kicks on then off after 10 seconds. This is the first time I ran the unit since it was serviced by a technician. Could this...


View more questions Search