    Oct 10, 2008, 06:27 PM
    Proper way to install copper pipe through basement wall
    I am putting a new water supply line in the older home we just purchased. There was a 3/4" galvanized pipe running from the city main to the water meter in the basement. I am replacing the galvanized pipe with 1" copper tubing. The galvanized pipe had rusted and holes in it where it went through the basement wall. What should I put around the copper pipe to protect it? What is code?
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #2

    Oct 10, 2008, 06:42 PM
    If you're going to increase to one inch then bore a 1 1/2" hole through the cement wall and sleeve the hole with a piece of 1 1/4" PVC. That's what we do. Good luck, Tom
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Oct 10, 2008, 07:03 PM

    Generally penetrations should be sleaved. Cut a piece of PVC pipe where the 1" pipe will pass through.

    Use cement and caulk for the PVC. Try to rent a core drill.

    Diameters you can figure out. Use schedule 40 tables for the PVC and 1" tubing tables for the "copper pipe" . It's really tubing.

    If you need more help, holler.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Install door in basement block wall [ 7 Answers ]

Hey Guys. My basement has no fire exit. I want to put an exit door in my basement wall so I can finish the basement into a rec room. It is an external load bearing block wall and has a 18"x12" window at the top of the wall with timber framing above. Bsically, I want to enlarge the window to fit...

Proper copper pipe soldering technique [ 3 Answers ]

What is the proper technique for copper pipe soldering. I do not see anything about deburring that the IRC code requires. I have seen on a welding site that soldering should be wiped clean to remove residual flux but that the pipe should be sufficiently cooled first otherwise the joint could cool...

Proper fasteners for copper pipe straps [ 8 Answers ]

When mounting sweated copper pipe to wood framing using copper pipe straps, what type of fastener should be used? I have always been confused about what causes the galvanic reaction between copper and steel. Are drywall screws OK to use? Thanks much for the advise. TWC

A/C not cooling, Small Copper pipe COLD and Large Copper pipe room temp. [ 4 Answers ]

I just moved into a newly constructed townhome and the a/c units are of course new. The A/c is not cooling at all. The machine inside turns on as well as the one outside. The inside A/C makes a strange sucking sound kind of like if you were sipping something out of a cup with a straw and you ran...

Copper pipe minimum depth in wall? [ 1 Answers ]

Howdy all, Is there a minimum depth that copper pipe must be installed within walls? In other words, minimum clearance between the pipe and the drywall? I know there is for electrical lines, so somebody hanging a picture doesn't drive the nail in and electrocute themselves. I have an...


View more questions Search