    Leaking AC Duct
    My AC duct coming out of the AC unit in the attic is soaked with water. It started to leak out and onto the sheet rock and is causing a leak in the ceiling. What is causing this?
    EPMiller's Avatar
    EPMiller Posts: 624, Reputation: 37
    Senior Member
     
    #2

    Sep 9, 2008, 07:33 PM
    Condensation is causing your problem. Most likely you have ducts that are not insulated and/or sealed correctly which is allowing warm humid attic air to come in contact with the cold duct. This will drop the temperature below the dew point and cause the condensation which then soaks the duct insulation and when that can't hold any more it starts to drip out at the low points which unfortunately is your ceiling.

    It sounds like you have a system retrofitted into your house. In my opinion, attics are the worst places to run ducts and do a good install. Current home retrofits usually use duct board for the trunks and flex out to the grills. The transition is a metal collar which, if the flex isn't carefully installed, will be exposed to the ambient air and consequently cause condensation when in the cooling mode. This not only is bad for your ducts and house, but also your wallet. You are trying to air condition the attic.

    You will have to inspect the ducts and find where the condensation is happening and then seal and insulate things until the condensation problem is cured. You might have to puncture the outer layer of the flex to let puddled water out so things can dry out or even replace sections of soaked duct and install it correctly. After fixing the water problem, you might have to cover the duct system in the attic with fiberglass batts to insulate it correctly so that you aren't losing so much energy to the attic. If the temperature at the supply grill fartherest from the AC unit is more than 3 to 5 degrees warmer than the supply closest to the unit, your ducts are NOT insulated correctly. Make certain you measure that on a good hot day. :)

    Good luck

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Duct fan [ 2 Answers ]

To the side of our house I added a bedroom and a bathroom. New area has an almost flat roof attached under the gutter of old house. The new floor is 27 inches lower than old floor. To get heat and air to new room I came off the end off trunk line in attic with a 90 dropped 27 inches and turned...

Flexi Duct vrs Aluminum Duct [ 4 Answers ]

I am adding an addition onto my house. The local building inspector has already told me my HVAC unit is more than adequate in size to support the addition. The old duct vents are aluminum. Can or should I use flexi venting in the new part? What are the pros and cons of these two types of vent...

Duct Condensation [ 1 Answers ]

:confused: I have a vent in an upstairs bedroom that won't stop leaking. The furnace is in the attic almost above the room. The main duct from the plenum leads to the first duct which leads to the room in question. Upon removing the register grill, I sealed all around the "boot". In the...

Ac unit leaking from duct [ 6 Answers ]

I have water coming from the bottom of the duct work that is just past the ac unit itself in my attic. The pro says that I have a roof leak. WE CANNOT FIND WATER ANYWHERE FROM OUR ROOF. The top and sides of the ducts are dry... the bottom is where it is wet. The tape is wet and dripping onto my...

Return Air Duct [ 3 Answers ]

I rent a townhome. It has 2 air conditioning units. I don't know what brand they are. The upstairs does not cool very well. It is always warmer than downstairs. The return air unit is in the storage closed downstairs. There are 2 return air ducts. The one downstairs was covered up behind...


View more questions Search