    Specific wire needed
    I am running 100 amp service from my panel in my basement 250 feet underground in 2" conduit to my polebarn. I am just trying to get all the supplies I need but do not know what wire I need.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Sep 11, 2008, 10:08 AM
    Sorry for the delay here but I missed your entry.

    For a 100 amp feeder, I would suggest you use a 100 Amp breaker. The conductors should be 3 #1 AWG (Copper) THWN conductors plus a #8 THWN conductor for ground.

    I do not believe that these conductors will fit into a Trade Size 2 conduit.

    I can check when I get home and have access to the NEC Code Book.

    By the way, what type of conduit are you planning on using? I also need to make sure that my calcs are correct.
    Tev's Avatar
    Tev Posts: 232, Reputation: 20
    Full Member
     
    #3

    Sep 12, 2008, 01:20 AM
    I assume you used PVC.

    If you have 1AWG wire and 2" schedule 40 PVC you can run 7 wires in it, for schedule 80 you can run 6 wires, so you will be fine with 2".
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Sep 12, 2008, 06:24 AM
    For grins, I priced out THWN #1 copper wire. The best price I found was $835 for a reel of 250 ft.

    So simple math, says that you would need 3 reels of #1 THWN wire ($835 X 3 = $2,505) plus a reel of #6 AWG copper THWN (ground) $635.

    So just to get from here to there is going to cost $3,140. Plus the cost of a remote 100 Amp panel box. A grounding rod, an Equipment grounding conductor. One 100 amp dual pole single throw Breaker.

    You may want to consider using an Aluminum feeder size #2/0 with a size #4 Ground.

    Now, will they fit into a trade size 2 conduit? Yes and No.

    Using Schedule 80 PVC size 2 you can get 3 #1 THWN copper and 1 #6 THWN for ground. If you choose to go to Aluminum then you will need to go to trade size 2 1/2 conduit.
    Tev's Avatar
    Tev Posts: 232, Reputation: 20
    Full Member
     
    #5

    Sep 13, 2008, 02:58 AM
    Out of curiosity, how did you come up with those conduit fill numbers donf?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #6

    Sep 14, 2008, 05:35 PM
    From T310.16 - 90 (c) 150 Amp THWN copper = #1 AWG,
    From T250.122 Min ground for 100 amp is #8 AWG. However I chose to use a #6 ground.

    Chapter 9, T4 gave the Trade Size 2 Schedule 80 PVC total area as 2.874 sq.
    in. For more than 2 conductors I can use 40% of the`total area. (2.874 X .4 = 1.150 <rounded up>

    Chapter 9, T5 gave the #1 AWG wire at 0.1901 sq. in. per wire. You would need 3 #1 AWG conductors. 0.1901 sq. in. X 3 = 0.5703 sq. in.

    Chapter 9, T5 gave the #6 AWG wire at 0.0726 sq. in. 0.5703 sq. in. + 0.0726 sq. in. = 0.6429 sq. in.

    Since 0.6429 is smaller than 1.150 the four wires would fit.

    I did not use the fill tables because I was using different size wires for the run.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Neutral wire needed [ 11 Answers ]

Hello. I just purchased 4 SPST LED rocker switches the other day. I am using a computer power supply to power the switches by paperclipping the 3rd (black-ground wire) and 4th (green-PS on) wires. My problem is that the LED does not light because (I am told) I need a white neutral wire to connect...

Wire needed for a 100 amp sub panel? [ 3 Answers ]

I am installing a 125 Amp Sub panel in a detached shed approximately 100' from the house. The subpanel has a 100 amp main breaker in it and I have a 100 amp breaker that will go in the main house panel to feed it. I will be using #4 copper THHN for my 2 hot conductors and neutral conductor and a #6...

Specific ignition key needed for 99 Honda Accord? [ 2 Answers ]

Do I need to use the ignition key I got with my Honda, or can I get a valet key made? Someone said they think the key has a chip in it. If so, can it be disabled? They want about $100.00 to make one I think.:mad:

Specific Examples Needed . New to accounting [ 1 Answers ]

Hello! Sorry to bother everyone but I need help badly! I am just now getting started in my accounting class and do not understand something ... revenues ... I am trying to make an income statement but when I get to certain parts I get confused ... So can someone tell me what exactly falls under...


View more questions Search