    Change from Honeywell heat, and Carrier AC tstat's to LUX tstat
    OK, here is the equipment:

    10 yr old Carrier A/C unit with Carrier non-programmable tstat with available connections:
    • DO NOT USE
    • R
    • Y/Y2
    • G
    • C
    • W/W1


    25 year old Pensotti oil fired boiler for baseboard heat with a simple Round Honeywell tstat

    I purchased a LUX TX1500 to control both units (I hope)

    The AC tstat had 2 wire bundles feeding it, RC, Y, and G fed the tstat from one bundle, and the white wire from the second bundle was connected to the C terminal, no other wires were used from the second bundle. (2) terminals were not in use on the AC tstat (DNU, and W/W1).

    The boiler was simply hooked up to the tstat with the RH (red), and W (White) wires.

    I fished the boiler control wires up through the same hole as the AC control wires.

    First attempt failed to provide any cooling (but the fan did run) here was the wiring configuration:

    RH to RH (red from boiler wire bundle)
    RC to RC (red from AC 3 wire bundle)
    (left the factory installed RC to RH jumper in place, this was a mistake)
    G to G (green from AC 3 wire bundle)
    Y to Y (white from AC 3 wire bundle)
    W to W (White from boiler wire bundle
    C from the AC 1 wire bundle was taped off

    In this configuration, the heat worked, and the fan of the AC unit worked, but the cooling unit did not kick in. After a few minutes the fan kicked off (the Tsats fan setting was on).

    Sat down and read the wiring diagram again and noted that I should have removed the RC to RH jumper. After removing the jumper the system still functions exactly as above (no cooling).

    Did I "cook" something by having the jumper installed? Where should I look first?

    Thanks for the help.

    Scott
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #2

    Sep 6, 2008, 08:58 AM
    Does your system have 2 transformers? 1 for the heat/boiler and 1 for the a/c? If not you need the jumper from rc to rh,,
    vsvier's Avatar
    vsvier Posts: 4, Reputation: 1
    New Member
     
    #3

    Sep 6, 2008, 09:04 AM
    Uhmm, not sure, how can I tell?

    As I said, they are currently 2 separate systems, heating , and cooling. I guess there would be 2? One for each?

    Thanks for the help.

    Scott
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Sep 6, 2008, 04:23 PM
    It is possible you smoked the transformer on the one system.

    See if the thermostat has 24 volts going to it on the RC leg and the RH leg. If not back track and find the problem. You were correct in removing the jumper with a two transformer system.
    vsvier's Avatar
    vsvier Posts: 4, Reputation: 1
    New Member
     
    #5

    Sep 7, 2008, 12:53 PM
    I do have 24 vac on both the heating and cooling legs (RC, and RH), So I will assume that both transformers are OK. Anything else I should know, or should look for? Should it be working as I've described the wiring? If so, maybe the Tstat is no good.

    Scott
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Sep 7, 2008, 01:03 PM
    Do you have 24 volts coming out of the Y1 at the stat when in the cooling mode? If so the problem is not in the thermostat if not then the problem is with the thermostat.
    vsvier's Avatar
    vsvier Posts: 4, Reputation: 1
    New Member
     
    #7

    Sep 7, 2008, 01:20 PM
    RC to Y =24vac
    RH to Y =11vac
    RH to W= 24vac
    rc to w = 11 vac

    I can only check this with the tstat face plate removed, there are no test points to try and check it while it should be operating.

    Scott
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #8

    Sep 7, 2008, 05:01 PM
    You may have to check it at the wiring on the inside unit.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Replace York Tstat with Honeywell - T wire? [ 11 Answers ]

I have seen many Tstat questions but couldn't find any relating to the T wire. I currently have a heating AC unit (York) that is a heat pump with Tstat number 2TH11704024. I tried replacing the York with a Honeywell RTH7400 5-1-1 programmable thermostat. Thinking I had checked all the wires I...

Replacement of Carrier Heat Pump Thermostat with Honeywell TH6000 series thermostat. [ 4 Answers ]

I have a Carrier Series 50QT Electric heat pump that still uses the original non programmable thermostat. I am trying to replace it with Honeywell TH6000 series programmable thermostat. The wiring on the existing Thermostat as follows: O - White, I am thinking this is the Reversing Valve? Y...

Trane XL80 not working after tstat change out to Honeywell 3100C [ 9 Answers ]

I just changed out my thermostat from an old mercury thermostat to a Honeywell 3100 which is supposed to work with a heat pump. After I hooked it up the first time it would only heat my house in Em Heat mode. In my attempt to get the thermostat to work in normal heat mode I "fixed it" to where...

Trane Heat Pump tstat replacement with Honeywell prog - wiring question [ 1 Answers ]

I want to replace my Trane Weathertron tstat with a Honeywell RTH7400 prog one. I have a Trane heat pump with aux heat. I've been poring over these thread piece-mealing some info the follow is the result. The old wiring scheme: X2 - black O - orange G - green Y - yellow T - tan/brown R -...


View more questions Search