    Changing out Old bathtub for New
    Bathroom project with some issues:

    I removed an old bathtub from my master bath and would like to place a new Kohler tub. After speaking with a local plumber, he said I need to change my existing P-trap (that is buried in cement (condo was built ~25 yrs ago) and this requires chiseling into the concrete around and may cause damage to the apartment unit below us. He didn't give specifics as to why other than we won't find any tub that could fit to the dimensions of the current drain location.

    Another plumber said there would be no problem.

    So I am now asking for help, here are the details.
    The current drain is a 1.5" metal drain (I think its iron?) that is attached to a p-trap buried deep into poured concrete. The center of the drain is located 2.3"-2.5" (I wasn't too exact) from the bare wall studs in front (no drywall in place yet, but we will be putting 1/2 or 3/4" cement board with Tile on top for the tub walls.) and exactly 16" from the one finished side wall.

    I am looking to install the Kohler Portrait 5' tub. Info found at: http://www.us.kohler.com/onlinecatal.../1022148_4.pdf
    And
    KOHLER: K-1108-RA: Portrait® 5' bath: Baths: Bathroom

    Is everything OK for this install or do I need to remove the P-trap? Any thing else I need to keep in mind for this install? Do we need to install anything under the tub before putting it down or can it sit directly on top of the flat concrete sub floor? Can I buy Grohe faucets and use a Kohler tub?

    Thanks in advance!
    Mike
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #2

    Sep 5, 2008, 05:03 AM
    Good morning Mike,
    The current drain is a 1.5" metal drain (I think its iron?) that is attached to a p-trap buried deep into poured concrete. The center of the drain is located 2.3"-2.5" (I wasn't too exact) from the bare wall studs in front (no drywall in place yet, but we will be putting 1/2 or 3/4" cement board with Tile on top for the tub walls.) and exactly 16" from the one finished side wall.
    Ya lucked out! Your Kohler will rough 16" off the side wall and 2 1/4"off the front plate. I don't know why plumber #1 told you that you had a problem unless he was figuring on the Kohler roughing in at 1 1/2" off the front plate and 15 1/2" off the side wall. This is a normal rough for older tubs. Good luck, Tom
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #3

    Sep 5, 2008, 08:53 AM
    Hi Mike:

    Not only will you be fine with measurements as presented, but the tub waste and overflow assembly has some adjustability (left/right and back) behind the tub so that if off by say a 1/2" or so this will allow you to align and join all... see picture below.

    Are you planning on installing a ledger strip on the back wall to support the back wall of tub? Also, are you planning on installing this tub in a bed of mortar or similar to reduce creaking, etc. associated with all acrylic/fiberglass units?

    Let us know if need info. On this...

    MARK
    Attached Images
     

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Child support changing due to Child custody changing [ 4 Answers ]

I am asking this on behalf of my friend in a big dispute right now. We live in Iowa. She used to joint custody of her children (although the exhusband never saw them at all). She worked full time in lending for years. She remarried. She had more children with her new spouse so in 2006 she quit her...

Bathtub leak [ 1 Answers ]

I have a bathtub leak I have a KOHLER faucet, my hot water knob keep turning past the stop. What must I do to replace the knob. >Moved from Forum Help<

Changing the outside unit vs. Changing the whole system [ 7 Answers ]

My outside unit leaks Freon and needs to be replaced. The system is about 9-10 years old. Initially, the contractor gave me a $2500 estimate to change the outside unit to a new Trane XR14. When the written estimate came, it included changing the coil and fan package inside (it's a ceiling unit)...

No water in bathtub [ 5 Answers ]

I recently instaled a new water heater and now no water comes out of my bathtub or my shower. What do I need to do to get this fixed.

Help! Under the bathtub... [ 1 Answers ]

We are putting in a new tub due to some leakage in the previous tub surround. When we pulled up the tub, the tub drain hooks to a larger drain. The top of this larger drain appears to be open. Is this to vent the drain? It appears that the toilet also hooks to this drain. What keeps the...


View more questions Search