    bends in main drain/vent stack
    I have a 4" cast iron main drain stack that comes out of the foundation and runs about 40' up through the roof. It is leaking and falling apart so I plan on replacing it, my question is can I go up 5' from the basement floor and punch it through a 18" thick brick wall with 2x 90* bends, run it verticle for 25' and then at the top bring it back to the original roof location with 2x 45* bends?
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #2

    Aug 29, 2008, 05:47 AM
    I have a 4" cast iron main drain stack that comes out of the foundation and runs about 40' up through the roof.
    What's this stack picking up on its way to the roof? How many fixtures?
    my question is can I go up 5' from the basement floor and punch it through a 18" thick brick wall with 2x 90* bends, run it verticle for 25' and then at the top bring it back to the original roof location with 2x 45* bends?
    Why deo you wish to change the position of the stack vent? Your two 90 degree bends make a "dogleg" and that's never good in drainage. If you're going to do that use sweeps instead of 90's. You may place as many bends in the vent stack as you wish as long as it's a dry vent and you slope it back to the drain line. Good luck, Tom
    briansrch's Avatar
    briansrch Posts: 7, Reputation: 1
    New Member
     
    #3

    Aug 29, 2008, 06:17 AM
    Basement slab - 1 toilet
    First floor - 1 full bath and kitchen
    Second floor - 2 full bath
    Third floor - 1 full bath with 2 sinks and both a shower and tub

    The stack vent is on the back side of the house, a 3 story addition was added to the back to add bathrooms (120 year old house). The connection between these add on bathrooms and the main stack is a maze of pipes because they tried to avoid punching through the old exterior wall to get to the main stack. The second floor drains into the first floor which makes a horizontal U shape to go through an old basement window that is 6' away from the main stack. Needless to say it doesn't work very well.

    Since all 4 bathrooms are in the addition it would be a lot easier to route the main stack through the addition (or add a second stack that Y's off the main stack) then punch several holes through the 18" of brick for each bathroom on each floor.

    I think I am a bit mixed up on terminology. When I said 90* bends I am thinking of those long sweeping 90* bends, not the hard sharp angled ones. Is this what you mean by sweeps?

    By dry vent do you mean that the fixtures need to be vented separately from the main stack?
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #4

    Aug 29, 2008, 06:56 AM
    I think I am a bit mixed up on terminology. When I said 90* bends I am thinking of those long sweeping 90* bends, not the hard sharp angled ones. Is this what you mean by sweeps?
    Yes! I would certainly use sweeps, (see image) rather then 90 degree quarter bends.
    By dry vent do you mean that the fixtures need to be vented separately from the main stack?
    I'm assuming the lower fixtures are vented correctly and don't just drain directly into the stack vent. The dry vent,( vent stack) starts 6 inches above the flood rim of the highest fixture on that stack. You may put vas many bends in a dry vent>(vent stack) as you wish. Good luck, Tom
    briansrch's Avatar
    briansrch Posts: 7, Reputation: 1
    New Member
     
    #5

    Aug 29, 2008, 07:14 AM
    All bathrooms and the kitchen are being redone so they will be vented correctly. Right now not much is done right.

    Lets see if I am understanding correctly. This main stack will be used for drainage for all 3 floors, the dry vent starts on the 3rd floor at the level of the highest flood rim. The stack below this point is a wet vent down to the point of the lowest fixture. At any point of the dry vent bends can be used but they must slope downward (I assume 45* or lesser bends required here). On the wet vent portion of the stack 90* bends are acceptable but 45* would be better.?

    Is the dual stack option to code? They are Y'd in the basement from a single drain and then Y'd back together in the attic for a single exit through the roof? My area follows the Uniform Plumbing Code.
    briansrch's Avatar
    briansrch Posts: 7, Reputation: 1
    New Member
     
    #6

    Aug 29, 2008, 07:28 AM
    I think I might have added some confusion in my reply. All fixtures on all floors will be vented separately from the main stack and tied back into the main stack 6" above the highest flood rim (where it would be considered a dry vent?)
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #7

    Aug 30, 2008, 07:44 AM
    Quote Originally Posted by briansrch
    I think I might have added some confusion in my reply. All fixtures on all floors will be vented seperately from the main stack and tied back into the main stack 6" above the highest flood rim (where it would be considered a dry vent?)
    You are correct!
    Vent Stack = The vertical section of drain pipe that's dry from the upper most fixture.
    Stack Vent = The vertical section of drain pipe that the fixtures discharge into.
    Actually they're all one piece of pipe. Good luck, Tom

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

OK to vent only through main stack in a small bathroom? [ 4 Answers ]

Hello, I will be totally gutting and redoing my home's only bathroom next month and am trying to iron out any problems now before I start ripping things apart. I have a few questions about the best way to do things... The main waste/vent stack is cast iron, and runs vertically through the...

Possible Blockage Main Stack Vent [ 1 Answers ]

The two toilets and the tub in the upstairs bathrooms are plugged and will not drain or flush. There is a gurgling sound when we flush or try to plunge the toilets. I have been told by a plumber that he thinks the main stack vent is blocked. How can I unstopped or clear the main stack vent? Are...

Drain line 5 feet long going into main stack [ 2 Answers ]

Hello, I am installing a washing machine drain line using 2" ABS pipe. The drain line will be installed within a 5 foot horizontal run going into the main stack. Within 5 feet of the main stack, do I need a vent line? Thanks for the help.

How do I tie into main vent stack? [ 3 Answers ]

Are there any tricks to put a 3" Tee into the main vent stack to add a lavatory? I don't think I can lift the top part of the stack up or push the bottom part of the stack down once I cut it in half but I think I'll need to seperate it by something like 2" and then push it back together to have...

How do I tie into main vent stack (cont'd) [ 3 Answers ]

Ok, I'm all new to this forum; my apologies for not giving you enough information! The soil stack (didn't know the difference between a soil stack and a vent stack until you explained it) is a vertical 3" PVC pipe and I'm trying to tie a 1 1/2" PVC pipe into that for the lav by using a 3" x 1 1/2"...


View more questions Search