Hello hvac1000,
Sorry to bother. I have posted a question this morning and followed some of the recommendations you had made previously to other owners of a trane xe80. May be you could help me out. I'm pretty sure that my problem resides in the 24V circuit coming out of the control board (White-Rodgers 50A50-471). For some reason there is no power going to the thermostat although there is 24V after the transformer (27V I measured). I opened the control board, but couldn't find any fuses there. I checked the drain pan switch and jumped the two wires and nothing...
How could I rule out the thermostat? Could the thermostat have blown due to the power surge? I can read the info, temperature is correct and it 'clicks' internally when I set it to cool/heat with the relevant temperature.
Thanks in advance for your time.
Inaki.
NOTE jump the thermostat out of the circuit.
Note your modual is nla but this one is close I think.If you have the open style board let me know.
http://www.white-rodgers.com/wrdhom/.../0037-6265.pdf
Trouble chart
http://www.white-rodgers.com/wrdhom/...pg0259_264.pdf
Thermostat
http://noblewinds.info/Hunter/ThermIns/44100.pdf
Jump the red to the green and the blower should come on.
Jump red to yellow and the compressor should work. NOTE!! There is a built in 4 minute time delay for the a/c to kick on at the thermostat so you will have to wait a few minutes to see if it works. NOTE hit reset as shown. See figure 5 on the thermostat paper I posted.
Now if you jumper at the board there should be NO time delay.
Please post here if any more questions.