    Splicing ground wires
    I'm installing a ceiling light fixture, romex in ceiling and stranded wire off the fixture. How do I splice the ground wires in order for them to attach to the green ground screw? I was thinking of crimping the stranded wire above the end of the romex ground and curling the romex ground around the screw. Is this a correct way to do this?
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Jul 30, 2008, 10:22 AM
    Wrap romex ground wire around ground screw leaving several inches sticking out, connect stranded fixture ground to end of romex ground with wire nut.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Jul 30, 2008, 11:25 AM
    Harold's way doesn't always work, so there are others. Sometimes you don't even have ground screws or the length of the ground is too short or it breaks off.

    One in particular, might interest you.

    A ground clip with a length of 14 AWG Solid wire. They are a real pain to install. If there are tapped holes available, you can use a ground screw and a length of stranded wire with a fork terminal on it. Bags of these are available at a hardware store. This will alow grounding of the box.

    There is another item which can be used and that is a green wire with a wirenut attached through the other end. This can then be attached to the Romex ground and the box ground and give you a free wire coming in the right direction.
    Tev's Avatar
    Tev Posts: 232, Reputation: 20
    Full Member
     
    #4

    Jul 30, 2008, 03:32 PM
    Or, get a spare length of solid wire and strip it at both ends, attach one end to the ground screw then put the other end in a wire nut with the ground wires.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Jul 30, 2008, 03:36 PM
    Or... do it this way...

    Quote Originally Posted by kbuchholtz
    I was thinking of crimping the stranded wire above the end of the romex ground and curling the romex ground around the screw.
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #6

    Jul 30, 2008, 03:51 PM
    Kbuchholt, you should be fine doing it the way you planned. Others just added some extra ways, just in case. Tk---> basically said the same :)
    kbuchholtz's Avatar
    kbuchholtz Posts: 110, Reputation: 2
    Junior Member
     
    #7

    Jul 31, 2008, 05:41 AM
    Comment on tkrussell's post
    I actually went this way, however wrapped the strand wire around the screw 3 times and tightened, rather than the romex. Thanks to all!
    kbuchholtz's Avatar
    kbuchholtz Posts: 110, Reputation: 2
    Junior Member
     
    #8

    Jul 31, 2008, 05:42 AM
    I wrapped the strand wire around the screw 3 times and tightened, rather than the romex after crimping the two wires with a splice cap. Thanks to all!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Ground Wires [ 28 Answers ]

OK... Im wiring up a detached building and I have ran into a small problem. Might be a dumb question but here goes. Im feeding from the box under my meter out to the shed. Im running 6/3 w gnd. I got the shed sub panel under control. But in the box under my meter for the fround wire, there is not...

Ground and neutral Wires [ 9 Answers ]

Is it proper to connect the ground and neutral to the neutral buss? I am installing a sub panel from a 200amp svc to a 125 service using 6g. My sub box does not have a separate ground buss rather only 2 neutral buses with a crossbar. I was informed that I can put the neutral and ground on that...

Old home with no ground wires [ 15 Answers ]

I'm changing out some 2 prong receptacles in an old home that has no ground wire (ie, the electrical cables have a hot and neutral, no ground wire). I'd like to install new 3 prong receptacles. Is this OK? What are the implications of doing this? Thanks!

Ceiling Fan Ground wires? [ 2 Answers ]

So I took my Aloha breeze ceiling fan apart again. Now I connected all the wires like the instructions say. I connected the black ceiling to the red remote, white ceiling to the white remote, the blue remote to the blue fan, black remote to black fan, white remote to white fan, and both green wires...

Wiring Ceiling Fan with Two Ground Wires [ 6 Answers ]

Trying to install a ceiling fan... From ceiling: white, black, green and copper wire From fan: white, black, blue and green Connected white.white, black & blue to black... QUESTION: Do I connect green from fan to green in junction box, or to green and copper in junction box? If...


View more questions Search