    Wiring for Honeywell ct-31 with R,G,W (cooling only)
    (I only need for this thermostat to control my Amana A/C unit).

    I did not record the old thermostat wiring before replacing with the new Honeywell CT-31 I have connected the R wire to R terminal; G to G Terminal; W to W terminal. This caused the thermostat to function partially but only when the thermostat switch was set to 'Heat'; the fan operates continuously regardless of temp setting - fan only powers off when switch is returned to 'off' position. Compressor seems to function properly but this is moot when using the Heat setting.

    I then moved the W to the Y terminal and now the fan unit seems to be functioning fine with the thermostat set to 'Cool' - the temp setting seems to control the A/C unit properly. The problem is that the fan continuously runs until setting back to the 'off' position manually (the temp setting only controls the A/C unit properly and not the fan).

    Do I need a jumper? Are the R,G wires on R, G terminal respectively, the problem?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jul 21, 2008, 11:20 AM
    Try moving the R wire to RC. The RC is for cooling the RH is for heating.

    Since you already moved the other from w to Y it should work.

    Post back with results.

    A copy of your instructions below.

    http://customer.honeywell.com/techli.../69-1809ES.pdf
    murphma's Avatar
    murphma Posts: 2, Reputation: 1
    New Member
     
    #3

    Jul 21, 2008, 12:06 PM
    There are only 4 terminals on the Honeywell CT31 tstat (R. W. G. Y.). There are not RC or RH terminals
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Jul 21, 2008, 12:13 PM
    Then you might try placing the G terminal with the wire on the y terminal. Do not jumper just put both wires under the y terminal.

    If you just jump them anytime you move the blower switch from auto to on it will cause the ac to run without thermostat control.

    By placing the g with the y whenever the thermostat calls for coolinhg it will also bring on the blower.

    The thermostat should have internal workings to do this but why yours is not working I have no idea.

    You can always call Honeywell on there toll free number.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How to wire 3 wire 2 zone cooling only to Honeywell thermostat [ 10 Answers ]

I currently have two zones for cooling only and the thermostat wires are red, blue and white. The red is labeled Rc which is easy, the white is labeled W Heat (this doesn't make sense to me) and the blue is labeled cool? What I think I need to do is connect the red to the Rc on the thermostat,...

Honeywell wiring different from old thermostat wiring [ 2 Answers ]

I purchased a non-programmable digital thermostat to replace an analog thermostat with wiring red, white yellow and black. How do I match the wiring? HELP!!

Replacing Honeywell T8411R with Honeywell RTH7500 - wiring problems [ 1 Answers ]

I need help getting my new, programmable thermostat to work. I currently have a dual-stage Heat Pump and A/C unit that works fine. The current thermostat is the Honeywell T8411R. I don't know the number for the subbase, but it's the one that came with the thermostat. The current (operational)...

Program honeywell RTH230B cooling system [ 1 Answers ]

I am having problems trying to program my cooling system to come on now. I tried with the programming of time, but that did not start the unit to come on. Thanks

Honeywell RTH110B not cooling [ 1 Answers ]

I am replacing a Janitrol HPT18-60 with a Honeywell RTH110B thermostat. I hooked up all the wiring accordingly with the 5-wire diagram as I have all five wires (y,g,r,b,w) and the heat will work, but the cooling will not. I have an outside heat pump. I also live in a mobile home if that makes a...


View more questions Search