    Low Voltage at lights using 2 3way switches
    My circuit includes 2 3way switches that control 2 lights. I have power coming into the first 3way switch with a 12/2 wire. The hot (black) is connected to the single common, the 2 travelers are connected to the 2 travelers on the second switch, then the common on the second switch goes through the 1st light, then to the 2nd light, then to the neutral (white) on the incoming power line. Problem: The switches are working the lights correctly; I have 110 volts going into the 1st switch but only have about 60v at the lights. Why, what’s wrong?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Jul 3, 2008, 10:07 AM
    You have the lights in series rather than parallel. 60+60 = 120. Each light drops 1/2 the voltage in the configuration you have.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Jul 3, 2008, 11:33 AM
    From PM:

    Quote Originally Posted by josborn
    Great, thank you - that makes sense.

    Now, to wire the lights in parallel, the neutral wire needs to not only be wired in, through the light and then back out but, I also need to jump over or past the light connecting on the other side as well..... right?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #4

    Jul 3, 2008, 11:36 AM
    Put the whites together on the first and second light and attach to neutral.

    Put the blacks together on the first and second light and attach to the (common of the second switch)

    I'm assuming that the lights have a black and a white.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How many 3way switches can be used in lighting circuit [ 4 Answers ]

Need to know how many 3way switches can be used lighting circuit

3way switches and motion sensor combination wireing [ 3 Answers ]

I would like to know how to wire up two 3way switches and motion sensor combined. Sequence of operation is as follows; when you walk in room motion sensor detects motion turns the lights on but you can also control the same flouresant lights by using the 3way toggle swithes so you basically have...

Disable a Motion Sensor on 3way Switches [ 2 Answers ]

I'm ready to "throw in the towel" on my outdoor floodlight, motion sensor operated by three-way switches. Most of the time the driveway just stays in the dark because the two different motion sensors I've tried are complicated to figure out on a 3-way switch. So I simply want to by-pass the...

Ceiling fan w/ 3way switches for light and 1 way for fan [ 1 Answers ]

I am replacing a ceiling fan that has 3 switches that control the light and 1 that controls the fan. I have 4 wires coming into the box for the fan (black, red, white and grnd). The new ceiling fan has a remote that has to 2 lead wires that are supposed to be connected to the source and 4 (2 for...

3way or 4 way switches? [ 2 Answers ]

I live in an old 3 decker that was recently rehab'ed and turned into condo's. There is a main stair way that runs up to serve the second and third floors. On each floor (main, 2nd, third) there is a light switch that when turned on, will turn on a hallway light on each floor. We want to...


View more questions Search