    Furnace fan won't shut off
    We have a 20+ year old forced air propane gas with central air. The air conditioning was just installed last year and things worked fine. But since we switched from heating to air conditioning the fan will not shut off whether the system is in "heat" or "cool" or "off" and the fan in "auto" or "on". We were told we probably needed a new fan/limit control so we installed a new one of these, but we still have the same problem. We also tried and new thermostat and that did not solve the problem either. Both the air conditioner and heater work its just that we cannot stop the fan from running other than shutting off the electrical breaker.

    Any suggestions??


    I would appreciate some help on this.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jun 22, 2008, 03:29 PM
    You might have a stuckA/C blower relay. Check the diagram on the inside if the blower door to see if it is listed. If that relay shorts closed it will cause the fan to run all the time. So will a fan and limit control but you already replaced that part.
    letmetellu's Avatar
    letmetellu Posts: 3,151, Reputation: 317
    Ultra Member
     
    #3

    Jun 22, 2008, 07:49 PM
    I would check the wiring at the terminals at the furnace, since it worked for the heating it sounds like a wire may be misplaced on the terminal board. Here is the way it should be wired, But the colors may not match your's so you may have to search it out:

    At the furnace it should be:
    Red on R
    White on W
    Green on G
    Yellow on Y

    Also there are two wires that go to the condensing unit the colors do not mater.

    One wire goes to the Y with the Yellow wire
    The other goes to the Terminal marked Com.

    The same applies at the thermostat;
    Red on Rh----with a jumper going to RC
    White on W
    Green on G
    Yellow on Y

    Good luck let me know if this helps

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Furnace won't shut off [ 2 Answers ]

My electric furnace was kicking the breaker and shutting down. I'd reset and it would work fina a week oe two then blow it again. Now it won't shut down. Is this a thermostat problem or something else.

Furnace will not shut off [ 3 Answers ]

Recently installed a noma programmable thermostat and same worked fine for four days but today the furnace would not shut off despite the temp rising to 78+F. The temp was set for 67F. The only way to get the furnace to stop running was to shut it off manually. How do I correct this problem?

Furnace will not shut off [ 1 Answers ]

I have a 20+ year old Coleman furnace with AC. The White Rogers thermostat has four wires connected, RC, W, G, Y. There in no jumber from RC to RH. There is a blue wire embeded in the wall but is not connected on either end. The AC worked great in hot weather. The problem now is that when the...


View more questions Search