    No power to home central AC
    My A/C unit was freezing up outside, got it serviced w/ 2 lbs of freon & then it started working fine. A week later, water dripped from the vent in the ceiling. I got a wet vac & sucked out the drainage pipes after finding puddles of water in my attic and mostly in the reserve pan. The pipes were in fact clogged.

    Now, there AC will not come on. I checked all the breakers & reset switches. No luck. It had been running fine through all of this...
    letmetellu's Avatar
    letmetellu Posts: 3,151, Reputation: 317
    Ultra Member
     
    #2

    Jun 18, 2008, 01:21 PM
    There is a system to trouble shooting AC troubles. If nothing is running, that includes the compressor, the condenser fan motor and the squirrel cage blower motor, you hunt for lose of power to the 120 volt part of the system, this problem sill usually be a breaker in the breaker panel, more than likely a 30 amp breaker.

    If you find that you have power going to the furnace, or air handler, then you look for a low voltage problem, This could be a bad thermostat switch, or a fuse on the circuit board, a loose connection in the low voltage wiring.

    If you have no problem inside the house, that is with the furnace or air handler then you go to the condensing unit and start looking for a problem there. If nothing out side is running you check for a blown fuse, this can be a fuse in a fuse box near the unit or a tripped breaker in or near the main breaker panel, or it could be both since sometimes they are double protected. If the outside blower is running but the compressor is not then you look for a problem in the unit like a bad compressor or a bad capacitor, a loose connection, a time delay device, and other problems that it could be that you would not be able to find.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Home central AC outdoor condenser unit blowing fuses [ 5 Answers ]

The unit is a Trane and is 22 years old and blew the 35amp dual element, time delay (current limiting) fuses that are in the little metal box on the side of my house next to the unit yesterday while running the AC during a hot day. I replaced them this morning with exact replacements and the new...

Central Heat Unit quit working after power outage [ 1 Answers ]

I have a Coleman gas powered central heat unit in a mobile home. It was working fine then we had an ice storm and lost power. Power is back on but furnace will not work. I have double checked the breaker switch and the pilot it still lit. The air conditioning part of the unit seems to be...

My Home needs POWER [ 1 Answers ]

I have a problem Im not much of a electrical person, so here's the question. I am putting a moblie home on my property Friday Oct 6 and I need power what should I get for a meter box weather head and underground cable to supply the trailer with enough power so I won't have to worry. And also do I...

Central AC won't come on following home inspection [ 2 Answers ]

I'm in the process of selling my house and a home inspection was just performed. Supposedly everything went okay and no problems with heating/ac were noted on the report. However, when I got back in town, the house was warm. The AC wouldn't come on when I adjusted the thermostat (on auto or on...


View more questions Search