    Flutter Valve Inside Wall Next To Toilet?
    In my basement bathroom, inside the wall next to the toilet stop valve, there seems to be some kind of flutter valve activated. I can hear air being released as the valve flutters 4-5 times in rapid succession, with about a 2 second pause between these cycles. I can also hear gurgling water as the valve is fluttering. What is the purpose of this valve? Use/non-use of the toilet and shutting off the stop value makes no difference. At this point I can't figure out anything that makes a difference. It comes and goes.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #2

    Jun 10, 2008, 07:09 AM
    I know of no such flutter valve in residential plumbing. All I can imagine is that someone installed a AAV instead of a vent stack which would not be allowed by code. If everything is working properly I'd ignore it for now but if a problem develops you will need to open the wall to investigate. Do you know if this bathroom is properly vented through the roof line?
    Thanos's Avatar
    Thanos Posts: 2, Reputation: 1
    New Member
     
    #3

    Jun 10, 2008, 02:40 PM
    The bathroom in question is directly below the main floor bathroom, which is vented to the outside roof. I just assumed the vents were connected. I climbed onto the roof and checked the pipe for blockage as far down as I can see and it looks clear.

    This may sound silly, but we did just get about 8-12 inches of rain over three days and my sump's been running nearly continuously for several days now. Could there be pressure in the system somehow related to all of that water in the ground?
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #4

    Jun 10, 2008, 05:41 PM
    The bathroom in question is directly below the main floor bathroom, which is vented to the outside roof. I just assumed the vents were connected.
    Bob nailed it!!
    You must run a separate vent for the downstairs bath. It can not use the same pipe as a vent,(vent stack) the upstairs bath uses as a discharge pipe,(stack vent) so instead of running up a separate vent and reventing in the attic the plumber installed a AAV, (Air admittance Vent) and tucked away it inside the wall. This is why every code going mandates a access panel so that when the AAV goes belly up like yours that it can be serviced. There's no doubt in my mind that your "flutter valve" is a AAV that's gone bad. Open up the wall, replace it and build a access panel in the wall so it can be serviced in the future. Good luck, Tom

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Leak inside wall [ 1 Answers ]

I live in a lower unit in a condo building. My upstairs neighbor had her water heater go out and it leaked inside her closet for a couple of days before she realized what was happening. The first day it leaked, I noticed a rivulet of water coming through the seam of my tub surround, which is...

Drain vent ends inside wall? [ 1 Answers ]

I recently had my house supply water lines replaced. At that time I asked the plumber if he could rough in a sink in the garage. I was about to replace the insulation and seal up the sheetrock hole where he added the new pipes when I noticed the drain vent pipe goes about 5 feet up the inside of...

Broken Toilet Vent Stack inside wall? [ 4 Answers ]

We had a leak in our roof. The roofer said it occurred at the one of the exits for the vent stacks on the roof and fixed it. However, he "fixed" all the others. Right after he left I went to flush one of the toilets and it now sounds as if we are next to niagara falls. The bathroom backs up...

Venting into an inside wall [ 1 Answers ]

We are building a YURT. We are building rooms inside. We do NOT want to put any holes in the walls or roof for the bathroom vent, but DO want an inside bathroom. Would it work if we vented between the walls? Where we live, a composting toilet is not an option. Thank you for any advice on how...


View more questions Search