    PEX retrofit now has low pressure
    I am helping a friend with a Remodel of a hundred year old house, the main water lines were Iron, and rotting through, so the main lines to the second story were replaced with 3/4" PEX from a 3/4 copper in the basement. The line from the basement runs around 15 feet and then are split on T's reduced to 1/2 "and run to the different fixtures. There is no manifold, and I am thinking this may account for the low pressure. The lower level seems to have good pressure, the Pex is already run to the second story, and there is no budget to rerun with Copper. Does any one have any ideas on how to resolve the issue?
    EPMiller's Avatar
    EPMiller Posts: 624, Reputation: 37
    Senior Member
     
    #2

    Jun 9, 2008, 07:06 PM
    I doubt that copper will solve your problems unless you find a crimped tube when you are tearing the pex out. Water pressure is reduced approximately 1 psi for every 2 feet of vertical rise. So if your second story fixtures are 10 feet above your first floor fixtures they will have about 5 psi lower pressure. Now if you dropped to 1/2 in pex too quickly, if you have long runs of half inch and several tees in them, then yes, you will have pressure problems. A quick and dirty rule is run 3/4" to the last tee in the line and 1/2" for any branches to a single fixture. This is wasteful on the hot lines however. The plumbing code book will give you the correct way to calculate supply sizes.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What is a window retrofit permit [ 1 Answers ]

What is a retrofit window permit. I would like to replace my large 3 windows with two smaller windows. It will require adding a few cinder blocks to close in some space. I have a feeling the window retrofit permit only permits windows Of the same size in the replacement. Because it...

Retrofit gas valve [ 2 Answers ]

I have a Rheem gas furnace that's about 25 years old with a standing pilot gas valve. I want to replace the valve with a Honeywell spark ignition model; I can do the replace but how do I wire the control circuit for this unit? I have a camstat fan limit switch, two wired from the thermostat, a...

Foundation j bolt retrofit [ 4 Answers ]

House has never had any tie down j bolts on The mud sill. However concrete blocks are hollow and usually They fill down two blocks with mortar and place the J bolt in the wet mortar poking up through holes You bore in the mud sill. Can I cut out the face of the block on one web, Put the j...


View more questions Search