    Ac condenser unit compressor won't turn on
    I've got a problem I need help with. I just installed a condensing unit outside for my air. It was empty when I got it. No refridgerant. When I start the unit the fan and all comes on but the compressor does not. This is a duroguard 2.5 ton unit. I have tried to boost it and still no luck. The unit is only 1 year old. Is there any way anyone can help me troubleshoot this thing and help me solve it. I have all the tools I need (gauges, vacuum pump,freon,etc.)
    Please helpl its so hot in the indianapolis area.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Jun 6, 2008, 07:30 PM
    First, make sure you have power in and out of disconnect(240 volts?), then for outside unit to kick on you need 24 volts from AHU, Transformer and thermostat to provide 24 volts to contactor. If no 24 volts to contactor coil, it is a control problem, Contactor can be manually overridden for testing, to check compressor operation.
    mint5jf's Avatar
    mint5jf Posts: 2, Reputation: 1
    New Member
     
    #3

    Jun 6, 2008, 11:07 PM
    OK here are my thermostat wires so I can make sure I have them right.

    Furnace colors-
    Red
    White
    Grey
    Brown

    Thermostat wires-
    Green
    Blue
    White
    Red

    Ac unit wires-
    Red
    White

    Please confirm for me that I have them right by telling me which wires go where.
    Thanks so much
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #4

    Jun 7, 2008, 06:12 AM
    On thermostat (R)red is 24 volts from transformer, (W)white is Heat, Green(G) is Fan, Yellow or blue is cool. A multimeter will confirm switching of thermostat,
    When set to cool, red connects to Yellow or blue(verify)for the compressor contactor, and also (G) green for blower motor.
    In Heat, red connects to (W)white for Heat strip contactor and (G) for blower motor.
    When set to Fan only, red connects to (G)green/blower motor only.
    Yellow or blue will connect to red or white for Compressor, other wire(white or red connects inside Air Handler(other secondary wire from transformer).
    Since wire colors are different, use gray for green, and brown for blue, then red is red and white is white.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Fan blade on my unit won't turn [ 8 Answers ]

My fan blade on my central unit won't turn. It appears it is trying to turn, so I helped it with a screw driver. The fan blade then runs with out fail, but will not cool. I was told that it might be my capacitor? Why is it when the blade turns it won't blow cold air?

A/c unit outside won't turn on byitself, thermastat? [ 6 Answers ]

My family went on a trip to see relatives in the country. When we came back the a/c had quit. The inside blower motor works, just the outside unit will not turn on. Everything is fairly new, except for the thermastat on the wall, which is one of those old round mercury like switches. I took the...

Outside unit fan won't turn [ 2 Answers ]

I have just moved into a home with an older heat pump, sometimes when the heat comes On in the house the outside unit makes a loud humming noise but the fan does not turn I am new to heat pumps so I don't know if this is normal or not. Any help offered would be appreciated.

Outside unit won't turn on [ 1 Answers ]

My outside unit Ruud 10 seer won't come on. I looked closely and noticed that some of the thermostat wireing had been cut most likely by digging dogs. Anyway I have a yellow blue white red and green wires leading from the house but only yellow purple blue and brown at the unit which wires connect...

Air handling unit won't turn off. [ 13 Answers ]

Hi, I have moved into new offices and had new server rooms kitted out and went for geothermal cooling, it uses a massive air handling unit to supply the cool air to the server cases but the air handling unit won't stop, I even hit the emergancy stop button on the main control unit. But it Won't...


View more questions Search