    a/c shuts off temp never reached
    My heat pump will run cooling mode for only about 30 min. or so. Then the outdoor unit shuts off. The indoor fan keep blowing. The smaller line going into the evaporator freezes between the evaporator and a valve with a capillairy tube that leads to the larger line. Once it thaws which takes about 20 min. the outdoor unit starts again. Temp in house never reaches 75 which is what it's set too. When it runs it does blow nice and cool I just need it to run longer.

    Thanks
    Phil
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #2

    Jun 5, 2008, 06:31 PM
    The low pressure switch is opening the circuit as a safety. You are low on refrigerant or you have a restriction in air flow= dirty: filters,blower wheel, evaporator coil, restriction at metering device at evaporator coil and or a bad blower motor.
    firebirdlt1's Avatar
    firebirdlt1 Posts: 3, Reputation: 1
    New Member
     
    #3

    Jun 5, 2008, 07:09 PM
    Quote Originally Posted by firebirdlt1
    My heat pump will run cooling mode for only about 30 min. or so. then the outdoor unit shuts off. the indoor fan keep blowing. the smaller line going into the evaporator freezes between the evaporator and a valve with a capillairy tube that leads to the larger line. once it thaws which takes about 20 min. the outdoor unit starts again. temp in house never reaches 75 which is what it's set too. when it runs it does blow nice and cool I just need it to run longer.

    Thanks
    Phil
    Thank you for your help. My filter is new. I will check the blower wheel and evaporator coil. If that does not fix my problem I will call a tech to check if the system is low. It was low last year but he could not find a leak. If it is low again I guess they will have to look harder. :)

    Thanks
    Phil
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #4

    Jun 5, 2008, 07:28 PM
    If it was low last year and the leak was not fixed it will be low this year. If they can't find the leak have them add dye to the system, it won't lie it will tell you exactly the place of the refrigerant leak.
    firebirdlt1's Avatar
    firebirdlt1 Posts: 3, Reputation: 1
    New Member
     
    #5

    Jun 13, 2008, 01:45 PM
    Service tech checked pressure said it looked fine then it started to drop after about 15 min. of running. The coil froze and the system shut down do to low pressure. The tech cycled the rev valve a couple of time saying it might not be fully seated in cooling mode. It ran for 45 min, then after he left it froze again starting at the coil and moving out to the Thermostatic expansion valve. Then the system shut down again. I'll have to call them back out again, but I'd rater not. $$$$ any other ideas for me to check before I whip the ol' pocket book?
    Thanks
    Phil
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Jun 13, 2008, 05:36 PM
    Yea call him back. He did not fix it the first time so the service call should be free.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Cycling on-off before desired temp is reached [ 2 Answers ]

GMP100-3 gas furnace: The furnace runs for 3-5 minutes then shuts itself off for 2-3 minutes then repeats the start- stop cycle. I turned the thermostat up but it still acts the same. Any tips would be appreciate

Furance shuts off before themostat temp is reached [ 1 Answers ]

Hi, I have a new two stage variable speed lennox furnace, G61V-60C-091. Due to some heating problems right after the install, the company I hired also installed a new white-rodgers programmable thermostat 1F78. Unfortunately even with the new thermostat, I'm having the same problem. At 6:15am,...

I set the temp, heat kicks on for 30 seconds, then shuts off [ 5 Answers ]

I know next to zilch when it comes to my heating and air system, so that's why I'm kind of led to believe this may be something simple. We have natural gas heat for our home. Lately, it's been a little cooler in the day so I've set the thermostat for about 73 degrees and switched the system over...

Furnace won't maintain temp - shuts off [ 5 Answers ]

Furnace problem - Turn temp to 70 Furnace runs until 70 degrees Maintains temperature for awhile - probably for a couple of hours At some point it stops maintaining the temperature and keeps kicking on and off. I've watched the thermostat - I'll actually turn the temp up to try to get it to...

Carier furnace shuts off before reaching temp [ 2 Answers ]

I have a carier weathermaker furnace that shuts off before reaching temp. any idea what could be the problem.


View more questions Search