 |
|
|
 |
New Member
|
|
Jun 4, 2008, 01:00 PM
|
|
New A/C water leaking from unit in attic not from pipes
We have a new heat and A/C unit in the attic. Had it put in last fall. Turned the air conditioning on and after about 30 or 40 min. water starts leaking through the ceiling onto the floor below. The water is coming from the empty box like thing that is next to the evaporator (I hope I have that word right). We've looked at the pipes and none of them are leaking. Since the unit is new we don't expect that any pipes are clogged. This part of the unit has insulating material all around it. We can't get anyone out to look at the unit quickly... hard enough just to get someone to call us back... we are in a rural area. Is there anything we can do?
|
|
 |
Heating & Air Conditioning Expert
|
|
Jun 4, 2008, 01:27 PM
|
|
Try to free up the drain. It is probably plugged up. Gently back flush just a bit from the discharge end to the unit.
|
|
 |
Uber Member
|
|
Jun 4, 2008, 02:13 PM
|
|
In a proper install a water switch should have been installed in that location and an overflow drain pan.
|
|
 |
New Member
|
|
Jun 4, 2008, 02:35 PM
|
|
Thanks for quick response. The overflow pan is under the evaporator but not this part of the unit which is empty and directs the cold air to the trunks. To try and picture it, there is the blower, the evaporator and then the section that directs the air. You're saying that this part of the unit needs an overflow drain pan? Just to make sure I've included enough information.. . this part of the unit has insulation all around it and is where the water is dripping from. Insulation is now wet on the bottom.
Water switch: all the switches are 'on'. I don't know if one of them is called a 'water switch'. All help is appreciated.
|
|
 |
Ultra Member
|
|
Jun 4, 2008, 05:59 PM
|
|
Not being able to see its hard to say what to do,but it does sound like a drain line is stopped up,, I allways put evap coil ,furnace and all in a overflow drain pan, but the pan also needs a drain put in it to back up the main drain,, sounds like the installer needs to come back and maybe do his job over again
|
|
 |
New Member
|
|
Jun 5, 2008, 06:29 AM
|
|
Have read the links. Thanks for sending. We found a rip in the insulation on the area that leaked. The tear exposed that section to the hot air in the attic. We're rewrapping and taping.
No water in either drip pans, pipes leading out have been slanted down. Will check for stoppage in drain pipes also. Sweating like pigs but carrying on. Will post pic. If all fails -thanks for explain how to do this.
|
|
 |
New Member
|
|
Jun 5, 2008, 08:08 AM
|
|
Here is the attachment with picture of the unit in the attic.
|
|
 |
New Member
|
|
Jun 15, 2008, 05:49 AM
|
|
Resolution: The problem is being resolved slowly. The unit was not level. So even though the common answer to this problem has been 'clogged pipe' a unit that has not been leveled properly will not allow the condensed water to flow out through the pipes and out of the house. All of the pipes were dry right from the pan. It's a bad installation. We have had the installers come to the house and level unit. There has been no dripping water through ceiling for a few days but just checked the unit and the secondary pan is filling up with water and isn't letting the water flow out and down the pipes leading out of the house.
I figure the secondary pan shouldn't have any water in it at all.
|
|
 |
Uber Member
|
|
Jun 15, 2008, 12:50 PM
|
|
Yep, secondary pan should have no water. It should be equipped with a water switch that prevents the AC from turning on if it does, so you'll investigate when you have no AC.
|
|
 |
New Member
|
|
Jun 18, 2008, 09:50 AM
|
|
Final answer. Installers came back. Opened unit / evaporator. The first drip pan was cracked. Water was not being fed from this pan down the pipe and out of the house (for anyone who doesn't know this by now). Instead it was leaking into the secondary drip pan. They replaced the cracked drip pan and so far no problem. Also installers did put in a cut off switch for secondary drip pan - no cost. Thanks for all help and comments.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Water leaking from blower unit
[ 1 Answers ]
Tempstar furnace 11 years old, on third blower motor, replaced "O" rings between blower unit and furnace and made sure drain line is clean and still getting water under unit.
Do I need to replace another blower unit?
Location of water pipes in attic
[ 3 Answers ]
I am trying to locate the water pipes in my attic. I went up and moved insulation around by where the water heater pipe should come up but no pipes. How do I find them? Thanks
Leaking copper hot water pipe in ceiling between in attic of 2nd story home
[ 1 Answers ]
March 9th 2008, has leak in copper hot water pipe. Pipe is between the 2nd story ceiling and attic. Had is repaired by licensed plumber same date.
New leak discovered today (a week later - March 16th) same copper pipe, but different location. About three feet removed from first leak.
Home is...
Hot Water Pipes Might be Leaking Somewhere
[ 2 Answers ]
Normally you have to let the hot water run awhile in my bathroom to get the water hot. Now it is hot instantly which leads me to believe there is a leak somewhere; however, I looked at all the usual places... no leaks. I have a four year old water heater which seems to be operating properly. I...
Drain vent leaking water in attic and onto ceiling
[ 13 Answers ]
I noticed a leak on my bedroom ceiling and traced it to a drain ventilation system looping though my attic. It does not seem to be connected to the main vent stack. It seems to be leaking at an elbow joint.
The drain vent is PVC and I'm guessing is connected to my tub and washer drains and...
View more questions
Search
|