    Circuit breaker loads
    How many conductors (of the same size) are allowed per circuit breaker? I thought more then one as long as the load requirements were met. A friend told me he thought only one wire (circuit) per breaker; is this a NEC rule? :)
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    May 24, 2008, 12:29 PM
    You could have several wires pigtailed and have 1 wire on breaker. And don't know of a limit, except wires in a wirenut, then you could go to a second and 3rd wirenut.
    Only 1 wire wire can be on breaker.
    If I am wrong, we will both know shortly.
    Only time I see a need for this is If 1 receptacle in each room was on a back up circuit, each would be homerun from multiple connections, or Smoke Detectors.
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #3

    May 24, 2008, 08:30 PM
    Some breakers are only rated for 1 conductor, some are rated for 2 or more. It depends. Yes, it's an NEC rule. See NEC 110.14 for more information.

    Basically, both you guys are correct!

    Rate this answer!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Theory of vacuum Circuit Breaker & sf6 circuit breaker [ 15 Answers ]

I want to know about the basic Theory of vacuum Circuit Breaker & sf6 circuit breaker

Replacing Circuit Breaker with Higher AMP Breaker [ 8 Answers ]

Excuse me, I did look at the code book as is suggested in your Sticky. The NFPA may answer this question, but I am not knowledgeable enough to recognize it: Our offices are upstairs in an older (renovated home) building with modern wiring. We have 4 computers, 3 printers, and miscellaneous with...

Main Breaker loads [ 4 Answers ]

I am trying to figure the capacity of my breaker box. Looking at the main breaker and lugs, there is two sides. So my question is, if the main breaker is a 100 amps; is the capacity of the box 100 amps per side (being 200 amps total), or 100 amps total and only 50 amps per side. The breaker...

Circuit breaker [ 3 Answers ]

A circuit breaker connected to the kitchen tripped twice. I had an electrician in but the problem persists - in fact, the very day the electrician came. It does not seem to be caused by any one particular appliance. The first time I was using the waste disposal and the next two times nothing was...

Replacing a circuit breaker with a GFI breaker- q on neutrals [ 1 Answers ]

In process on installing withquestion on neutral wires. Do you take the neutrals out of the in the main panel neutral and put them in into the breaker where its labelled "load neutral terminal" and only have the neutral "pig tail" to the panel neutral bar? Thanks!


View more questions Search