    Converting 240V to 120V
    I decided to go with a gas dryer and will be removing the 240 receptacle and replace it with 120. Can I use the heavy gauge wire already in place along with the circuit breaker, which is 50 amps or change it?:confused:
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    May 19, 2008, 02:46 PM
    You can cap unused hot at both ends, #12 pigtails wirenutted to the #10? to allow wire to fit on breaker and on receptacle. Then you need a 20 Amp single pole breaker for protection.
    If needed you can reidentify 1 of the hots at both ends wit white tape and will be the neutral.
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #3

    May 19, 2008, 03:57 PM
    If needed you can reidentify 1 of the hots at both ends wit white tape and will be the neutral.
    Please present a code reference that permits re-identifying the ungrounded conductor to white in this case.

    To the OP,

    Do you have copper or Alum wiring?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    May 19, 2008, 05:57 PM
    Quote Originally Posted by Stratmando
    If needed you can reidentify 1 of the hots at both ends wit white tape and will be the neutral.
    Yeah, that's definitely a no-no for #10!

    A #10 neutral MUST be white all the way.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #5

    May 19, 2008, 06:46 PM
    Ninicruz,

    Back to the start. You are allowed to use only the Black, White and ground conductors. Although, if it not too much of a task, you might want to consider replacing the current conductors with 12 AWG, which is rated for 20 Amp.

    You will need to get a permit since you are changing a circuit within the Main panel.

    The 50 Amp Dual Pole breaker has to be removed, That is not an option! Replace the breaker with a 20 amp single pole/single throw breaker for your new circuit. The conductor size for 50 AMP is #6 AWG conductors, not # 10 AWG. Personally, I would not recommened using #6 conductors to carry 20 Amp. You can do it, but #6 AWG is really thick and hard to work with. You must also get a slot cover that will fit into the main panel's cover to block off the open slot left by removing the 50 Amp Breaker.

    In the Main Panel box: If you choose to use the existing conductors, you can cap off the red lead. Leave the White and Ground where they are. Connect the black lead to the new 20 amp breaker. (DO NOT INSTALL THE BREAKER YET)

    At the outlet end: Remove the existing 50 amp faceplate and receptacle. Cap off the Red lead. Connect the black, white and ground to the new outlet. Install the new receptacle and faceplate in their proper positions.

    Go back to the Main Panel and install the breaker, turn it on and test the circuit. If everything is working fine, call the AHJ and have the work inspected.

    Keep the inspection approval with your home owners insurance papers.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

120V or 240V for heaters? [ 6 Answers ]

I apologize in advance for seeming daft :confused: , but I am still missing the 120V vs. 240V issue for small appliances such as room heaters. There seems to be an advantage of 240 V only when you may be pushing your circuit; I gather one can put twice as much wattage (e.g. heaters) on a 20A...

How to tap 120V out of 240V heater circuit [ 9 Answers ]

Hello, I need to tap 120V out of the existing 240V baseboard heater wirings to use a 120V 3-prong washer (the heater itself was removed, only the wiring left. I do have a 120V outlet nearby but on the other side of the doorway so I don't want to use it) Currently there are 5 wires at the 240V...

120v to 240v [ 5 Answers ]

Hello! If anybody could help me with this it would be great. I'm looking at buying a festool saw from america which runs on 120v but tools and electrical equipment in austraila run on 240v. Is there anything I can do to make it work and if so is it going to be a hassle??

240V/20Amp to 2(120V/?Amp) [ 1 Answers ]

I have a 240V line with max load 20Amp. If I split each of the hot 120V leg sharing the neutral and ground to 2 individual 120V outlet/receptacle, what would the max amp load of each? Does it sill maintain 20Amp? Or reduce by 1/2? Is there a formula to this? Thanks.

120V heater tape off a 240V source. [ 3 Answers ]

Hi, My question is very similar to HandyJohn's and much my question was answered in is post. Mostly verifying my suspicion of needing a step down transformer here. Just wondering if you know of any simpler options I may be overlooking outside of running a dedicated line. Here's my...


View more questions Search