               Junior Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      May 8, 2008, 12:23 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
      
      
        
        Installing a new bathtub
       
      
    
    
    
                  
        I hope that this is a relatively simple question. 
 
I am converting a bedroom into a bathroom.  I am going to be installing stone or ceramic tile and a combination bathtub/shower.   
 
Because of the tile, I will be installing 3/4" plywood and then 1/4" cement board as underlayment. 
 
I will definitely need to put the plywood under the bathtub, but do I need to install the cement board under the tub also? 
 
Thanks!
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                | 
            
      
              
               Senior Plumbing Expert 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      May 8, 2008, 04:43 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        Hi frazwood: 
No..no need to install the cement board under the tub.  In fact, I use the 1/4" cement board (and tile) to kind of LOCK the tub in place.
 However, I don't push the concrete board up to the tub... instead I keep the cement board about an 1/8th inch off tub and then tie it all together by filling this 1/8th inch space with thinset mortar or modified thinset mortar.
 
Which raises point... you should be using a 1/4" notch trowel with thinset mortar or modified thinset mortar to install the cement board to the plywood... use hardibacker and hardibacker screws if available in your area... then want to tape the joints using alkaline resistant tape and thinset mortar.
 Check out this site for more information:
 James Hardie: HardieBacker 1/4'' backerboard        Check out under  FLOOR INSTALLATION
And what kind of tub Fraz..  If this is going to be a fiberglass or acrylic unit you should plan on installing the tub/shower unit in a bed of mortar or similar... makes a huge difference in terms of creaking, flexibility, etc. (here would set tub in substrate, fill tub 1/2 to 3/4 of the way with water, let dry 24-48 hours and then drain the tub, step in.. and you will be impressed by solidness! ).   Let me know if need more information on this.
 
Let me know what you think... Mark
 
.
      
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               Junior Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      May 9, 2008, 04:34 AM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        Mark: 
 
Thanks for the help.  Your answer makes (using the cementboard to help keep the tub in place).  I have my hardibacker, hardibacker screws, 1/4" notched trowel, and tape  ready-to-go (I'm installing cementboard in another room before the bathroom). 
 
I was definitely planning on installing the tub in a bed of mortar (I was going to follow the installation directions provided with the tub... which say to do just that). 
 
Tim
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                | 
            
      
              
               Home Repair & Remodeling Expert 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      May 9, 2008, 01:14 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        Mark has given you some good info here. Do you have good access to the area directly below the old bedroom and have you pulled a permit from the city yet? Keep us informed as this project progresses, it's the kind we especially like.
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               Junior Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      May 11, 2008, 03:59 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        
	
		
			
			
				
					  Originally Posted by  ballengerb1
					
				 
				Do you have good access to the area directly below the old bedroom and have you pulled a permit from the city yet? Keep us informed as this project progresses, its the kind we especially like. 
			
		 
	 
 Yes, I have access below the old bedroom.  It should be a relatively straight-forward project, although I've never done anything like this before... 
 
I have pulled a permit.  I have a rough-in electrical inspection tomorrow and then a framing/rough-in plumbing inspection once I complete the plumbing. 
 
I'll try and keep y'all updated.
 
Thanks!
 
Tim
      
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               Junior Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      May 22, 2008, 10:33 AM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        
	
		
			
			
				
					  Originally Posted by  massplumber2008
					
				 
				And what kind of tub Fraz...?  If this is going to be a fiberglass or acrylic unit you should plan on installing the tub/shower unit in a bed of mortar or similar...makes a huge difference in terms of creaking, flexibility, etc. (here would set tub in substrate, fill tub 1/2 to 3/4 of the way with water, let dry 24-48 hours and then drain the tub, step in..and you will be impressed by solidness!!).   Let me know if need more information on this. 
 
Let me know what you think...Mark 
 
. 
			
		 
	 
 I am now in the process of installing the tub but I am not going to use mortar because the installation instructions specifically state not to do this (I was incorrect in my post above).  The body of the tub does not actually touch the floor.
 
I am not 100% sure, but I think it's an American Standard Princeton Recess tub.
      
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                | 
            
      
              
               Senior Plumbing Expert 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      May 22, 2008, 02:10 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        Hi Fraz: 
 
Thanks for update... hope all goes smoothly... ;) 
 
Can you tell me what the manufacturer recommends setting the tub in..  Something... nothing?  
 
Thanks.
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               Junior Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Jun 19, 2008, 02:42 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        
	
		
			
			
				
					  Originally Posted by  massplumber2008
					
				 
				Hi Fraz: 
 
Thanks for update....hope all goes smoothly...;) 
 
Can you tell me what the manufacturer recommends setting the tub in...?  Something...nothing?? 
 
Thanks. 
			
		 
	 
 Sorry for the delay in responding... 
 
The manufacturer's instructions clearly state to not set the tub into ANYTHING.  In fact, there is a large sticker on the tub that tells the installer of the tub that setting the tub into concrete, mortar, or the like will void the warranty.
 
A brief update on things... 
 
I passed my plumbing/framing inspection earlier this week.  My wife installed the tile on the floor yesterday.  The next projects are installing the wallboard (non-tub area) and hardibacker (tub area) and then to install the tile around the tub.
 
It'll take a few more weeks, but hopefully I'll post some pictures when it is done.
      
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                | 
            
      
              
               Senior Plumbing Expert 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Jun 19, 2008, 03:13 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        I'll tell you... no mortar under tub is a first for me... especially in terms of VOIDING warranty!  
 
Thank you for that information!  I will review the literature to see why this is so... ;) 
 
Good luck on the rest!  
 
Mark
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                | 
            
      
              
               Eternal Plumber 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Jun 23, 2008, 09:54 AM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        Some manufactures have support already installed under the tub but didn't know it voided the warranty to add more support. Mark if you pull the installation information let me see it please and why vwasn't this thread moved to the Plumbing Page?  Regards, Tom
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                | 
            
      
              
               Senior Plumbing Expert 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Jun 23, 2008, 10:34 AM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        May want to ask Bob that one, Tom... ;) 
 
And as soon as Fraz. Confirms the tub name for me I will look it up and let you know!
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               Junior Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Sep 30, 2008, 02:58 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
         
Hey Guys: 
 
It's been a long time, but I thought that I'd give you the final update from this one. 
 
The tub was definitely an "American Standard Princeton Recess" tub. 
 
I installed it without mortar and so far it's been great.  I am attaching pictures of the entire bathroom. 
 
(by the way, I didn't post this in plumbing originally because I didn't ever intend to ask a plumbing question... it was more about tile/flooring). 
 
Anyhow, thanks to everyone for the help. 
 
Tim
     
     
    
      
      
    
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                | 
            
      
              
               Senior Plumbing Expert 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Sep 30, 2008, 03:21 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        Looks great Tim... nice job!  
  
That tub is a cast iron tub... yes?  
  
Thanks for update tim. 
  
MARK
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
 
 
 
     
  
   
  
  
   
  
  
  
  
  
  
  
  
  
  
  
  
  
  
    | Question Tools | 
    Search this Question | 
   
  
    | 
    
    
    
     | 
    
    
    
    
    
     | 
    
   
   
   
    Add your answer here.
    
    
 
Check out some similar questions!
Bathtub leak
 [ 1 Answers ]
TWTMC, 
 
     When I have the bathtub running,water drips down through the kitchen ceiling. 
I have removed the sheetrock to uncover the wood planking. What do I 
Do now to detect where the leaks coming from and remedy it. I had also 
Flushed the toilet and ran the sink vanity a no of times and...
 
 
Help!  Under the bathtub... 
 [ 1 Answers ]
We are putting in a new tub due to some leakage  in the previous tub surround.  When we pulled up the tub, the tub drain hooks to a larger drain.  The top of this larger drain appears to be open.  Is this to vent the drain?  It appears that the toilet also hooks to this drain.  What keeps the...
 
 
Installing new bathtub and fixtures... 
 [ 7 Answers ]
Hi 
My wife and I just began ripping out our old bathtub to put in a new one. We decided we would also like new faucettes etc. I disconnected the hot and cold taps but the shower pipe will not come loose. Is this a soldered pipe? It appears to have a nut on it but I can't get it loose at all.  
Any...
 
 
Installing a bathtub on a concrete slab
 [ 3 Answers ]
I have a toilet in the basement with proper vent. I want to add a bathtub near the toilet. After I jackhammer up the concrete and install the tub trap and drainage into the toilet drain, how do I seal the floor under the tub? The outside part is open and it should be easy to pour concrete mix and...
 
 
Installing a bathtub on a concrete slab
 [ 1 Answers ]
I am installing a tub to existing plumbing, but it's on a concrete slab. We've jackhammered the concrete so that I have enough room underneath to put in the drain and p-trap, but am I going to have to buy the tub, set it in place, hook up the plumbing and then remove it to replace the concrete?
 
 
 
View more  questions